Lithium battery build a few questions and problems

TommyDKY

New Member
Joined
Nov 18, 2020
Messages
9
Built a battery using 8 CATL 271AH 3.2 volt cells. I top balanced them to 3.6v in parallel. After this I built 2- 12v batteries and put them in parallel to yield 542ah with both batteries using a 120A overkill solar bms. Took out my 3-8D agm’s and installed the 2 lithium batteries and wired in parallel to my RV. Haven’t camped with them yet but trying to put them through a few paces.

Any suggested improvements on my setup are greatly appreciated.

Changed my Xantrex sw3000 inverter to an AGM profile that with 2 stage charging with bulk/absorption@14.2v and float @13.45. It does not have a lithium profile or a custom profile. Do you guys see any problem with that setup?

Installed a victron DCDC 30A battery charger to replace the isolator on the RV to charge the start and house batteries. Confirmed that alternator was pushing out only 14.1v for charging of start batteries.

I installed 1120w of solar last year and chose to use two victron 100/50 solar controllers w/560w on each controller with room to expand. Pulled the MH out into the sun to see how my lithium’s would charge by solar. Had the Solar controllers set to float @ 13.4v. Turned on inverter and a floor fan and left overnight. Let charge the next day with solar and checked on later in the afternoon and had one battery bms report the following

Monitoring the batteries with Victron BMV712 and Overkill solar 120A BMS on both batteries.

#2 high voltage cell overvoltage.PNG
Needed to investigate this anomaly (didn’t think the voltage should have been over 13.4 or much closer). So I decided to turn the batteries off using the BMS. But did not turn off solar controllers breaker or Battery breaker. My mistake I think??

Returned to check on the next day late morning. Noticed on Victron app that solar controller #1 front was not showing up and turned breaker on and off and it popped back up on the screen. Voltage was back down where I thought it should be
#2 voltage ok.PNG
Went back later that day and #1 solar breaker was popped again and even after reset couldn't get #1 to show on Victron App. Didn't have time to mess with it so came back the next day. Took off cover on breakers and saw this
burnt wire copy.jpg
And this is my original setup of controllers
Solar Controllers mounted copy.jpg

Here is what I think may have happened. I thought it was charging funny and didn’t have time to investigate so I used my bms to turn off charging to the batteries but I didn’t turn of the solar controllers or flip the solar breakers to off. The back panels were shaded by a building so it had no problems but the front panels had full sun and was trying to force that into batteries that were shut down. So going through the PV breaker into the solar controller then out of solar controller to battery breaker but the front battery wasn’t accepting it? That’s my guess at explaining it and why one breaker wire burnt and the other didn’t.

Does that sound like a plausible cause?

Why would there be a voltage discrepancy with the Victron BMV 13.52V(that is connected to the positive post of the batteries and neg to the load side of the shunt) and the meter 13.21V that is connected to the positive and negative post of the battery?voltage discrepancy copy.jpg
 
The heat looks like it came from the termination to the breaker. Would seem to indicate a poor connection generating heat.
 
x2

redo - tin copper cable ends then re terminate and watch, does it get warm to the touch under load? Does it smell funny?
 
I would recommend not to re- tin cable ends, the terminals are not designed for that as they are designed to clamp the conductor bare or with a Ferrel , for if you have another loose hot terminal with tinned conductor the solder runs out and makes the terminal hotter, i would suggest these terminals you have were loose , saying that this cable is on a 63 amp breaker , but is that cable 63 amp or smaller cable, saying that i do understand thats a 50amp charger but the circuit breaker is there to protect the cable and could be part of the issue,
does below circled in red indicate that current was flowing in the burnt cable and if so can this cable carry the 48 odd amps under a loose connection ?

Hope that helps, if the terminal are burnt out and annealed do not reuse but you maybe lucky so keep an eye on them as Boondock Saint suggests , also when fitting cables in terminals twist and double back ends to fill the terminal up if possible then tighten up tight , this is generally a better connection than even using a feral can give , the feral prevents flexible conductors from spreading but unless its fitted properly it can also be a problem

hope i have not confused you

1623749124832.png
 
I would avoid turning the discharge off at the BMS. There have been some strange things posted when that option is used. The FET's get really hot.

Regarding the crispy wire, it looks like the wire may have been inserted into the terminal at an extreme angle. I tried to get all my cables aligned perfectly inline with the terminal. I also used ferrules on all the cables that went into terminals like that. As suggested above, it could have been a bad connection at that terminal. That's where I would start. Replace the cable for sure, maybe the breaker. Give yourself a little more length on the cable so you're not making such a tight corner.
 