MPP LV6048
I'm having 2 problems with a new installation.
1) PV voltage drop from 80-85v to 65v-70v and from 36 amps to 20-25amps when I turn on the solar panels breakers.
2) PV2 input disconnects after a couple of minutes. Needs to restart the inverter (cut all power) for it to work again.
I have 8 39v 9.32amp solar panels. They are connected in 2 sets of 4 panels. 2 panels of each set connected in series to achieve 80v-85v and 18-20amps.
I'm having 2 problems with a new installation.
1) PV voltage drop from 80-85v to 65v-70v and from 36 amps to 20-25amps when I turn on the solar panels breakers.
2) PV2 input disconnects after a couple of minutes. Needs to restart the inverter (cut all power) for it to work again.
I have 8 39v 9.32amp solar panels. They are connected in 2 sets of 4 panels. 2 panels of each set connected in series to achieve 80v-85v and 18-20amps.