diy solar

diy solar

mppt max input voltage

masbango

New Member
Joined
Oct 22, 2020
Messages
22
Have mppt controller max 150v pv input. with 6 500w 48v 10.23a panel in serial and parallel

so total voltage is 144v .

question: is the total V to risky as maybe it can cross over 150v when have much sunlight,

Awaiting your reply

Bob
 
Have mppt controller max 150v pv input. with 6 500w 48v 10.23a panel in serial and parallel

so total voltage is 144v .

question: is the total V to risky as maybe it can cross over 150v when have much sunlight,

Awaiting your reply

Bob

MPPT Voltage limit is NEVER EXCEED, and you must allow for cold temperatures. Cold temperatures make panel Voc higher, so you will exceed 150V @ 15°C and lower.

2S3P only
not 3S2P
 
MPPT Voltage limit is NEVER EXCEED, and you must allow for cold temperatures. Cold temperatures make panel Voc higher, so you will exceed 150V @ 15°C and lower.

2S3P only
not 3S2P
thank you for your reply.
Can you illustrate me how to connect panels in 2S3P configuration for not exceeding 150v max?
Awaiting your reply

Bob
 
All explained here,
Discussion here,
 
Have mppt controller max 150v pv input. with 6 500w 48v 10.23a panel in serial and parallel

so total voltage is 144v .

Bob
You need the actual panel specs. If at maximum illumination power, the panels are Vmp of 48.0v x 10.23a Imp, their Voc will be about 56.5 vdc. If that spec is correct, it may be referenced at 40 degs C temperature or 25 degs C temperature depending on manufacturer spec sheet.

This reference temperature effects the temperature delta to your particular location coldest temperature you need to consider when applying the panel's voltage delta per degC temperature coefficient spec (typically about -0.3% to -0.4% per °C).

You need to stay within 150v controller limit at cold temp Voc. Morning time in cold weather is usually worse case situation since temp is coldest and there has not been much sun illumination time to warm up panels.'

Many SCC's will not start up on a cold morning if the input Voc gets too high. This is to help protect the unit from overvoltage. The MOSFET breakdown voltage of their DC-to-DC converter is greater when they are not switching so checking Voc before it starts up in the morning provides some extra protection against overvoltage input. Some SCC's have disconnect relays to panels which provides even better protection than just the MOSFET switching.

When a charge controller does an MPPT search the panel voltage can approach unloaded Voc voltage.
 