I'm looking at the documentation for the MultiPlus 24/2000 there seems to be a discrepancy in recommended cable sizes vs. fusing.
The 24/2000 manual specifies a 200A fuse on the DC input but then goes on to give a recommended cable cross section of 35mm². The Wiring Unlimited booklet in the DC wiring section also presents an example of a 2400W inverter load at different battery voltages, where the 24V input cable is carrying 100A and gives a recommended cross section of 35mm².
My understanding is that fusing and cables should always match the maximum amperage on that branch of the circuit. So if the 24/2000 DC input expects to potentially handle 200A, then that implies the cabling and fuses between the inverter DC input and the batteries (and the battery bank itself) should also be capable of 200A. Yet they recommend 35mm² for the cables, which should only be capable of sustaining 100A.
What am I missing here? Which maximum amperage value is correct?
The 24/2000 manual specifies a 200A fuse on the DC input but then goes on to give a recommended cable cross section of 35mm². The Wiring Unlimited booklet in the DC wiring section also presents an example of a 2400W inverter load at different battery voltages, where the 24V input cable is carrying 100A and gives a recommended cross section of 35mm².
My understanding is that fusing and cables should always match the maximum amperage on that branch of the circuit. So if the 24/2000 DC input expects to potentially handle 200A, then that implies the cabling and fuses between the inverter DC input and the batteries (and the battery bank itself) should also be capable of 200A. Yet they recommend 35mm² for the cables, which should only be capable of sustaining 100A.
What am I missing here? Which maximum amperage value is correct?