My Multiplus 24/2000 arrived today and I'm preparing to wire it up.
Our off-grid PV system is a 2kW into two BB batteries in series for a 24v.
No grid back feeding will be done but I'll take advantage of the incoming AC to provide an uninterruptible AC supply hopefully with solar priority.
After reading the Multiplus manual and understanding some of it my immediate concern is sizing the cables and disconnects (breakers) and fuses.
Tell me if this is wrong and suggest the correction;
Cable size- batteries to Multiplus= #2 copper welding cables about 2 feet long...maybe 3 feet.
Multiplus grounding cable to earth ground= #2 copper welding cable about 2 or 3 feet.
AC- in to the Multiplus= 14/2 with ground
Breaker before AC input= 15A (breaking the hot wire only)
AC- out of the Multiplus to the load subpanel= 12/2 with ground
Breaker(s) sub panel for output= 2- 15A breakers
The Multiplus has an internal fuse on the battery + input.
Am I missing details or proper requirements?
Any recommendations? (I want this to be a safe installation)
Our off-grid PV system is a 2kW into two BB batteries in series for a 24v.
No grid back feeding will be done but I'll take advantage of the incoming AC to provide an uninterruptible AC supply hopefully with solar priority.
After reading the Multiplus manual and understanding some of it my immediate concern is sizing the cables and disconnects (breakers) and fuses.
Tell me if this is wrong and suggest the correction;
Cable size- batteries to Multiplus= #2 copper welding cables about 2 feet long...maybe 3 feet.
Multiplus grounding cable to earth ground= #2 copper welding cable about 2 or 3 feet.
AC- in to the Multiplus= 14/2 with ground
Breaker before AC input= 15A (breaking the hot wire only)
AC- out of the Multiplus to the load subpanel= 12/2 with ground
Breaker(s) sub panel for output= 2- 15A breakers
The Multiplus has an internal fuse on the battery + input.
Am I missing details or proper requirements?
Any recommendations? (I want this to be a safe installation)