First time system builder here and want to bounce a few things off the group if I may. I wired up the following setup a few weeks ago:
- 1x MPP LV-MK 3048 all-in one
- 12x HQST 100W 12V monocrystalline panel wired in 6S2P configuration, 6 panels in each series and 2 series in parallel.
- 2x 24V 100ah Ampere Time wired in parallel
In optimal conditions under heavy load I'm pulling maximum about 780-790 watts or about 65% of the rated panel output. I live in Southern California and I've tested on multiple days, multiple times per day and I'm convinced that this is not because I'm not getting optimal conditions.
I'm reading about 100-110 volts input at the inverter and my clamp meter shows 10.2 amps coming in on the PV wires to the inverter. It shows very similar readings at the roof. I was expecting around 11-12 amps based on the ratings of the panels so I'm not sure if that indicates a problem at the panels or not. I tested each panel individually and it seemed to be producing to specifications.
My question is whether my 6S2P configuration could be problematic for a 48V system. My battery wants to be charged at 57.6V and I have that set in the configuration for the inverter, could it be a problem that the 100-110 volts I'm giving the inverter (which falls within their 60V - 115V MPPT voltage range specified in the manual) is not optimal and I'm losing power because of it?
I was considering re-wiring to 4S3P but I don't want to go through the hassle if it doesn't have any logic as to why it might work better.
Should I be concerned that I'm reading about 10.2 amps on the cables coming off the roof which seems to be less than I expected based on the specs of the panels?
Any tips on where to go from here to improve my situation?
- 1x MPP LV-MK 3048 all-in one
- 12x HQST 100W 12V monocrystalline panel wired in 6S2P configuration, 6 panels in each series and 2 series in parallel.
- 2x 24V 100ah Ampere Time wired in parallel
In optimal conditions under heavy load I'm pulling maximum about 780-790 watts or about 65% of the rated panel output. I live in Southern California and I've tested on multiple days, multiple times per day and I'm convinced that this is not because I'm not getting optimal conditions.
I'm reading about 100-110 volts input at the inverter and my clamp meter shows 10.2 amps coming in on the PV wires to the inverter. It shows very similar readings at the roof. I was expecting around 11-12 amps based on the ratings of the panels so I'm not sure if that indicates a problem at the panels or not. I tested each panel individually and it seemed to be producing to specifications.
My question is whether my 6S2P configuration could be problematic for a 48V system. My battery wants to be charged at 57.6V and I have that set in the configuration for the inverter, could it be a problem that the 100-110 volts I'm giving the inverter (which falls within their 60V - 115V MPPT voltage range specified in the manual) is not optimal and I'm losing power because of it?
I was considering re-wiring to 4S3P but I don't want to go through the hassle if it doesn't have any logic as to why it might work better.
Should I be concerned that I'm reading about 10.2 amps on the cables coming off the roof which seems to be less than I expected based on the specs of the panels?
Any tips on where to go from here to improve my situation?