I have four Chins 300ah LifePO4 batteries parallel by busbars, each #2 red wire with one 100amp inline circuit breakers. Charge by three EPEVER Tracer4215BN, each connect to 600w Solar Panels (3S2P), three charge controllers parallel by another set busbars with #4 wires, between each red wire with one 60amp inline circuit breakers too. And the 3rd set busbar use #2 wires connect to charge control's busbar and battery's busbar, plus my 1500w inverter, and 12v socket. The weird things is, each MT50 show different battery voltage, higher current higher voltage, for example, 30a 14.2v, 24a 14.0v, 13a 13.8v, this make charge controls enter floating earlier. I need either change all setting to higher voltage, remove one charge control or block few solar panels to make it work. How to solve this problem? Why everyday noon, when amp start getting higher voltage also getting higher (but not actually battery voltage, because battery only 70% full) What do I do wrong?