I have no problem trusting quality equipment.
But, I also agree that redundancy is beneficial.
I used to be a belt and suspenders kind of guy. But in my old age, I tend to spend more time in just boxers. lol
Ok mine setup without 120V split phase. Not sure how to set the load center box.
It is safe to put all AC and DC breakers next to each other? no electric arc?
It would be a better fit, yes.
I chose 125a, because it will handle the 150a surge.
It's good to know the trip curve of a breaker.
The higher the amperage, the less grace period before it trips.
It would be a better fit, yes.
I chose 125a, because it will handle the 150a surge.
It's good to know the trip curve of a breaker.
The higher the amperage, the less grace period before it trips.
Got it. It doesn't matter even the battery banks reached 600-800A right?
Noticed some folks here has breaking cap rated 10k-25k in case of surge from large battery banks.
Got it. It doesn't matter even the battery banks reached 600-800A right?
Noticed some folks here has breaking cap rated 10k-25k in case of surge from large battery banks.
Make sense. Do you use SPD or combiner box for panels to inverter?
I'm plan to use this 32A 1200V but most people pointed out 25A is sufficient? and noticed you use 63A?
SPD, yes.
Combiner box, never.
Breaker is just being used as a disconnect. Anything will work as long as it is rated higher than what is going through it.