Comparable product here might be a gypsum concrete. https://en.wikipedia.org/wiki/Gypsum_concreteGravel might be a bad translation, the German term is Schüttung. No idea how to convey it proper into english
Makes more sense to me, thanks.
Comparable product here might be a gypsum concrete. https://en.wikipedia.org/wiki/Gypsum_concreteGravel might be a bad translation, the German term is Schüttung. No idea how to convey it proper into english
Oh my gosh...that is way too funny. Thank you! ?rotating phone sideways should show signatures
Up North and Off Grid – Medium
Read writing from Up North and Off Grid on Medium. Off Grid at 63 degrees north in Finland. Every day, Up North and Off Grid and thousands of other voices read, write, and share important stories on Medium.medium.com
similar, but no the same but I'm not in building science, just a home-owner with radiant floor heat .Comparable product here might be a gypsum concrete. https://en.wikipedia.org/wiki/Gypsum_concrete
Makes more sense to me, thanks.
there is a vapor barrier underneath the slab. Otherwise a long time German builders designed their buildings around "Breathability" Not very energy efficient, but long lasting. So there are ventholes in windows, and the roof is usually vented. No airtightnessNo vapor barrier?
It's a small one at 1000 gallons.That boiler is interesting. How much water does is have in it?
Do you operate it like I do mine? You can probably get the storage water much hotter than I can in my home built tank using ICF blocks.It's a small one at 1000 gallons.
Water temp below 180 is due to it being an unpressurized system. The fire box in the tank you run the risk of boil.Do you operate it like I do mine? You can probably get the storage water much hotter than I can in my home built tank using ICF blocks.
EG: I build 1 or 2 fires per week. It takes about ~6 to 8 hours to go through 3 big arm loads to get my storage tank is up to 160F. The next day I clean out the boiler, reload it and then cost for at least 3 days.
Thanks for the tip on The Radiant Floor Co. in Vermont. They were really helpful on the phone. We have a super simple radiant floor, one loop, one pump, one Differential Controller (to Rule them All, sorry, couldn't resist). The Differential Controller has one sensor on a water heater, and switches a Grundfos pump on and off at a set point. Unfortunately, the lowest set point is 100 F and the floor is usually 50-60 degrees, seems like the temperature difference is to wide to be efficient. Maybe more importantly, the high set point may reduce the number of times the pump circulates. Our heat source is hydronic solar panels so we only have a narrow window on winter days to heat the floor. Radiant Floor suggested we may only need a floor sensor which would be a cheap fix, rather than up-sell us to an expensive unit.When I built my place (Northern Ontario Canada) I chose to use a Frost Protected Slab Foundation with 4" of HD Foam underneath R20 and up the sides along with 2" thick foam wing perimeter which is 24" wide (prevents frost creep) which is then buried. Within the Slab is 7/8" PEX with no connections within the concrete. The slab mass works as an excellent "regulator" year-round, during winter I have very even heat throughout and everything is warm (no chilly bed to crawl into at the end of a long day) and I gotta say, stepping out of the shower onto a warm floor is real nice ! In Summertime the slab keeps the house cool as it will cool to 15C/60F and stay there and acts like a heat sink. To be fair though, my place is Hyper Insulated with 5.5" of solid foam in the walls and 8" of PolyISO Foam in the cathedral roof and the build method with Cool Roof system and Rainscreen siding prevents thermal gain from the exterior. This combo works well as the house has never gone over 26C/79F even when it is 40C/104F outside, I actually have away my portable commercial AC Unit.
I DIY'ed my Radiant System using a full kit from The Radiant Floor Company (Vermont USA) who not only helped design the layout & setup, they sent the critical setup (valves & controls) all pre-assembled and laid out on 3/4" plywood ready for mounting. All of the components are Top Quality Brands and the "kit" is complete for you to install. I HIGHLY RECOMMEND THEM as their Kits are Excellent, the Prices are Very Good and the Design & Support people are Outstanding. They offer a broad range of kits & setups for New Builds, Renovations & Retrofits as well as many Heat Options including SOLAR !
I use the Floor Sensor which is within a tube (7/8" Pex line actually) that runs to the center of my slab. I have it set so it starts heating at 24.5C/76F and stops when the floor / slab is at 25.6C/78F. Now I do have 4" of HD-Type-II EPS Foam under the entire slab and up the sides, as well as 24" side wings to prevent frost creep under the slab. Building Code only requires 2" of foam for an FPSF Foundation.Thanks for the tip on The Radiant Floor Co. in Vermont. They were really helpful on the phone. We have a super simple radiant floor, one loop, one pump, one Differential Controller (to Rule them All, sorry, couldn't resist). The Differential Controller has one sensor on a water heater, and switches a Grundfos pump on and off at a set point. Unfortunately, the lowest set point is 100 F and the floor is usually 50-60 degrees, seems like the temperature difference is to wide to be efficient. Maybe more importantly, the high set point may reduce the number of times the pump circulates. Our heat source is hydronic solar panels so we only have a narrow window on winter days to heat the floor. Radiant Floor suggested we may only need a floor sensor which would be a cheap fix, rather than up-sell us to an expensive unit.
The house we live in is 5 years old and the radiant floor heat is such a headache. We weren't the original builders as we just moved in 2 years ago but I already dread winters here. It's zoned in 5 areas. And the Northeast corner bedroom never keeps up. We live in South Dakota so it gets really cold here. -10 today and that room will drop to the 50s. That room and the other spare bedroom on the Northwest side are both carpeted. I imagine that is the issue. What I can't imagine is why the heck the builders would allow the owners to lay carpet if it causes the heat to be ineffective. Our living room had difficulty keeping up today too. That's stone tiled with a large area rug. Is that the issue there? The living room is much more insulated as the center focus of the house and I haven't noticed issues here before. But I was disappointed to see 66 degrees on the thermostat for the living room today. I'm tempted to put in a forced air furnace b/c the annoyance of radiant floor heat never keeping up is making me crazy. Anybody relate? Any tips? Suggestions? I feel bad wasting such expensive work but a 5-year-old house should not be having this many heating issues, right?I know it's not solar but it is a critical part of the entire energy system of our house. It allows us to heat our home and shop off grid with impressive comfort for less than 2 kWh per day plus a few arm loads a day of wood for the boiler. A little over 5,000 ft2 total that it's heating plus the domestic hot water.
I recently updated the 20 year old two wire heat only thermostats to mesh ones that I can program and control online and remotely plus updated to some better datalogging while I was at it. I had to update the zone controllers and when I was done I took a step back and thought there's probably a few folks that would get a kick out of this but even more that would like to take a shot at my workmanship. Ha
It may not look shiny and new but remember it's starting it's 20th winter now. Interesting note about those Grundfos circulators. They were at least 20 years old when I salvaged them from Carter era solar space heating project.
This is a primary / secondary loop with outdoor reset set up. It monitors outside temperature and varies the water temp it's sending to the floor accordingly.
View attachment 122497 heating/cooling company
Hmnn... Let's look at the easy things first. Can you monitor supply and return temps? Supply and return flows? What size is your house? Heat source?The house we live in is 5 years old and the radiant floor heat is such a headache. We weren't the original builders as we just moved in 2 years ago but I already dread winters here. It's zoned in 5 areas. And the Northeast corner bedroom never keeps up. We live in South Dakota so it gets really cold here. -10 today and that room will drop to the 50s. That room and the other spare bedroom on the Northwest side are both carpeted. I imagine that is the issue. What I can't imagine is why the heck the builders would allow the owners to lay carpet if it causes the heat to be ineffective. Our living room had difficulty keeping up today too. That's stone tiled with a large area rug. Is that the issue there? The living room is much more insulated as the center focus of the house and I haven't noticed issues here before. But I was disappointed to see 66 degrees on the thermostat for the living room today. I'm tempted to put in a forced air furnace b/c the annoyance of radiant floor heat never keeping up is making me crazy. Anybody relate? Any tips? Suggestions? I feel bad wasting such expensive work but a 5-year-old house should not be having this many heating issues, right?
Plenty to digest there. How is it zoned and how is each zone controlled? By room? Can you provide pictures of system? What is the square footage of the house and what is the btu rating of the boiler?The house we live in is 5 years old and the radiant floor heat is such a headache. We weren't the original builders as we just moved in 2 years ago but I already dread winters here. It's zoned in 5 areas. And the Northeast corner bedroom never keeps up. We live in South Dakota so it gets really cold here. -10 today and that room will drop to the 50s. That room and the other spare bedroom on the Northwest side are both carpeted. I imagine that is the issue. What I can't imagine is why the heck the builders would allow the owners to lay carpet if it causes the heat to be ineffective. Our living room had difficulty keeping up today too. That's stone tiled with a large area rug. Is that the issue there? The living room is much more insulated as the center focus of the house and I haven't noticed issues here before. But I was disappointed to see 66 degrees on the thermostat for the living room today. I'm tempted to put in a forced air furnace b/c the annoyance of radiant floor heat never keeping up is making me crazy. Anybody relate? Any tips? Suggestions? I feel bad wasting such expensive work but a 5-year-old house should not be having this many heating issues, right?
Anybody relate? Any tips? Suggestions? I feel bad wasting such expensive work but a 5-year-old house should not be having this many heating issues, right?
Key word is that it is a *radiant* floor. Carpet kills the radiant effect, so you need to rely on less efficient conductive heat transfer. That requires a significantly higher water temperature-- at least 3F, but it could be up to 10F.That room and the other spare bedroom on the Northwest side are both carpeted. I imagine that is the issue. What I can't imagine is why the heck the builders would allow the owners to lay carpet if it causes the heat to be ineffective.
If you compare the cost of adding some electric heat sources for your cold rooms to your installed radian't floor system it would be cheaper than a whole new furnace system. Forced air leaves cold areas too, and near the floor is always colder than the ceiling, if that is any comfort for you.The house we live in is 5 years old and the radiant floor heat is such a headache. We weren't the original builders as we just moved in 2 years ago but I already dread winters here. It's zoned in 5 areas. And the Northeast corner bedroom never keeps up. We live in South Dakota so it gets really cold here. -10 today and that room will drop to the 50s. That room and the other spare bedroom on the Northwest side are both carpeted. I imagine that is the issue. What I can't imagine is why the heck the builders would allow the owners to lay carpet if it causes the heat to be ineffective. Our living room had difficulty keeping up today too. That's stone tiled with a large area rug. Is that the issue there? The living room is much more insulated as the center focus of the house and I haven't noticed issues here before. But I was disappointed to see 66 degrees on the thermostat for the living room today. I'm tempted to put in a forced air furnace b/c the annoyance of radiant floor heat never keeping up is making me crazy. Anybody relate? Any tips? Suggestions? I feel bad wasting such expensive work but a 5-year-old house should not be having this many heating issues, right?
I think you also need to look at the delta-T between hot water supply and return to see how big of an issue you have. A low hydronic delta-T means you don't have much load and you are wasting energy heating up the water too high; you could either reduce flow or reduce temperature. A high hydronic delta-T means that the start of your loop has much higher heat transfer than the end, which can make for an uncomfortable house especially if the start of the loop isn't where you have the highest loads.It is written in lots of literature on radiant heat that it is more efficient to have a smaller difference, deltaT, between the temperature of the circulating water and the temperature of the slab. How much difference can it really make?
Currently, my system only circulates at 100 degrees and the floor is usually not above 60 degrees. We are operating on "if it ain't broke don't fix it", but if it would make a big difference I'd try to find a way to change the set points of the differential controller.
It is written in lots of literature on radiant heat that it is more efficient to have a smaller difference, deltaT, between the temperature of the circulating water and the temperature of the slab. How much difference can it really make?