The system consists of 8 Absolute GP 100G21 VRLA Batteries, I have them wired series-parallel, two sets of 4 in series in turn wired in parallel for a 24v system.
Q1: Assuming these are 1200ah batteries and the Rover has 'Nominal Battery Capacity' parameter between 0-9999 do I set it to 1200? Default for autodetecting 24v it is setting a value of 200.
Q2: All the defaults for charging limits seem too high. It is currently around 105 degrees f here so the manual for the batteries says 2.20 is the lower limit VPC. The batteries are 3 cell so my math puts the maximum charge voltage at 26.4 or 13.2 x 2, however the Renogy charge controller is defaulting up to 14v. What should I use for float/max/equalize settings for these batteries?
Q1: Assuming these are 1200ah batteries and the Rover has 'Nominal Battery Capacity' parameter between 0-9999 do I set it to 1200? Default for autodetecting 24v it is setting a value of 200.
Q2: All the defaults for charging limits seem too high. It is currently around 105 degrees f here so the manual for the batteries says 2.20 is the lower limit VPC. The batteries are 3 cell so my math puts the maximum charge voltage at 26.4 or 13.2 x 2, however the Renogy charge controller is defaulting up to 14v. What should I use for float/max/equalize settings for these batteries?