Howdy,
I am planning a system for my own use - using Victron materials.
Goal is to use stored energy ( 30 kWh batteries) as much as possible, but fall back to grid if the batteries run low. I do NOT want a typical grid-tied system, I need to keep things running when ( not if ) the grid goes out. Hence I am going to use quattros with generator input
reading this : https://diysolarforum.com/threads/2...ictron-multiplus-and-or-autotransformer.69797
seems to confirm my opinion that using an (Victron 100A) auto-transformer behind 2 stacked 5kW quattro inverters would limit my total total 110V load to 28A, no matter whether the 2 legs are balanced or not. Well, that's not going to work
220V, I only need for my heavy loads - well pump, baseboard heater, heatpump etc.
So, I think to separate out all 220V loads into extra subpanel(s) where 1 panel (in my garage) will have "mixed" 220 and low 110 V (lighting). 2 stacked inverters and AT.
For sure not exceeding that 28A limit on neutral
Then have an inverter (110V output) and subpanel for all household 110V loads
It's certainly more expensive, but IMHO a decent solution
Thoughts ?
Thanks
Oskar
I am planning a system for my own use - using Victron materials.
Goal is to use stored energy ( 30 kWh batteries) as much as possible, but fall back to grid if the batteries run low. I do NOT want a typical grid-tied system, I need to keep things running when ( not if ) the grid goes out. Hence I am going to use quattros with generator input
reading this : https://diysolarforum.com/threads/2...ictron-multiplus-and-or-autotransformer.69797
seems to confirm my opinion that using an (Victron 100A) auto-transformer behind 2 stacked 5kW quattro inverters would limit my total total 110V load to 28A, no matter whether the 2 legs are balanced or not. Well, that's not going to work
220V, I only need for my heavy loads - well pump, baseboard heater, heatpump etc.
So, I think to separate out all 220V loads into extra subpanel(s) where 1 panel (in my garage) will have "mixed" 220 and low 110 V (lighting). 2 stacked inverters and AT.
For sure not exceeding that 28A limit on neutral
Then have an inverter (110V output) and subpanel for all household 110V loads
It's certainly more expensive, but IMHO a decent solution
Thoughts ?
Thanks
Oskar