I have been trying to discuss this with Seplos support, but it's really tough.
Can someone here who has a setup with more than one battery pack validate this issue on their end?
The BMS will report the amount of energy charged/discharged; in my case, these values seemed way too high, so I did a test:
- restricted the charge current to 40A
- configured ESS to "keep batteries charged"
- observed values from MP-II (charging with ~35-38A, so roughly 2kW)
The values reported by Seplos are between 5-6kWh per hour, so roughly three times as much as I'd expect. That multiplier of three is curious, since I have three batteries in a pack. I'd appreciate if someone here could check their own setup for similar deviation.
Upgraded the firmware to v2.8 as advised by Seplos support which didn't change anything.
Can someone here who has a setup with more than one battery pack validate this issue on their end?