Hi all
I now have two 200A Seplos BMS, each with 16 280Ah Eve cells.
DIP switches are set as per the manual, ie pack 0 is all off except sw 5, pack 1 only has sw 1 on.
Pack 0 has Victron/SMA protocol selected
Pack 0 and 1 are interconnected with a standard RJ45 patch cable
CAN cable is connected from Victron Cerbo GX to pack 0 and the Cerbo is reporting an SHEnergy battery and the pack voltage and SOC are being reported.
I'm not sure if the two packs are communicating with each other in this mode - how do I tell?
And then there is the real problem - if I then connect the Seplos supplied white USB to RS485 adaptor to pack 0 and fire up Battery Monitor, it will only talk to pack 1.
I'd like to be able to see what is happening on both packs while the CAN connection is doing its thing.
If I change the DIP switches so that they are set as pack 1 and 2 (with sw 5 off on the first pack), then Battery Monitor talks to both packs at the same time (proving that the cables are all good).
So, is this possible, or does a multipack config with CAN to the inverter/GX preclude using Battery Monitor at the same time?
Many thanks
Kind regards
John
I now have two 200A Seplos BMS, each with 16 280Ah Eve cells.
DIP switches are set as per the manual, ie pack 0 is all off except sw 5, pack 1 only has sw 1 on.
Pack 0 has Victron/SMA protocol selected
Pack 0 and 1 are interconnected with a standard RJ45 patch cable
CAN cable is connected from Victron Cerbo GX to pack 0 and the Cerbo is reporting an SHEnergy battery and the pack voltage and SOC are being reported.
I'm not sure if the two packs are communicating with each other in this mode - how do I tell?
And then there is the real problem - if I then connect the Seplos supplied white USB to RS485 adaptor to pack 0 and fire up Battery Monitor, it will only talk to pack 1.
I'd like to be able to see what is happening on both packs while the CAN connection is doing its thing.
If I change the DIP switches so that they are set as pack 1 and 2 (with sw 5 off on the first pack), then Battery Monitor talks to both packs at the same time (proving that the cables are all good).
So, is this possible, or does a multipack config with CAN to the inverter/GX preclude using Battery Monitor at the same time?
Many thanks
Kind regards
John