I've got a question regarding when to pre-charge a 48v inverter.
My solar system is happily working now, it's got an SOK 48/100 connected to a Multiplus-ii 48/5000 and a Cerbo GX, and prior to turning it on the first time I did use a pre-charge resistor (50W/33R) and it worked like a charm.
However, at the time that I was putting the system together, I forgot about the VE Can to Can Bus cable for the battery to the Cerbo GX. Now, the cable is finally on it's way and I do want to plug it in, however, here is where I come across a situation that I am unfamiliar with.
Per the SOK manual, I need to turn off all loads (MPPT, Inverter, etc), then turn the battery off, and finally turn the BMS off. After that, I can connect the communication cables, and then turn the system back on.
My question(s) would be:
- Given that connecting the cables takes a few seconds, do I need to go through the whole pre-charge process again?
- If it is possible to answer, does anyone know approximately how long it takes for a capacitor to discharge to the point where the pre-charge is needed?
All I know is that the capacitor discharge rate is an exponential one, so it loses a lot fast, but then never hits 0, so I'm curious to know at what point they would need to be pre-charged or they will spark to hell and back again!
I hope that the question is understandable, I find it hard to explain in general so I'm sorry if it;'s a bit fluffy!
I've got a question regarding when to pre-charge a 48v inverter.
My solar system is happily working now, it's got an SOK 48/100 connected to a Multiplus-ii 48/5000 and a Cerbo GX, and prior to turning it on the first time I did use a pre-charge resistor (50W/33R) and it worked like a charm.
However, at the time that I was putting the system together, I forgot about the VE Can to Can Bus cable for the battery to the Cerbo GX. Now, the cable is finally on it's way and I do want to plug it in, however, here is where I come across a situation that I am unfamiliar with.
Per the SOK manual, I need to turn off all loads (MPPT, Inverter, etc), then turn the battery off, and finally turn the BMS off. After that, I can connect the communication cables, and then turn the system back on.
My question(s) would be:
- Given that connecting the cables takes a few seconds, do I need to go through the whole pre-charge process again?
- If it is possible to answer, does anyone know approximately how long it takes for a capacitor to discharge to the point where the pre-charge is needed?
All I know is that the capacitor discharge rate is an exponential one, so it loses a lot fast, but then never hits 0, so I'm curious to know at what point they would need to be pre-charged or they will spark to hell and back again!
I hope that the question is understandable, I find it hard to explain in general so I'm sorry if it;'s a bit fluffy!