I have a pair of EG4 240/50's with the same concerns here in Phoenix. My stuff is in a utility room off the garage, mounted to the western exterior wall. Insulating behind the cement board on just that wall made a tremendous difference in the ambient. I keep the door to the garage open with a harbor freight small shop fan blowing in (The ~$60 one). Hottest ambient I logged was right at 135F on a 118 degree day. Generally speaking the extremes are only a few hours. I was going to mini-split the room, but I changed my mind. The EG4's are rated to like 160F (w/degraded output), but batteries are to 140 anyway, so I'm going to finish insulating the rest of the walls, cut a 24x24 grille for the door, and put in a large roof fan, it can just blow in the attic, it's all right next to the gable vent. It only gets peak hot for about 3-4 hours a day.