You completely misunderstood my point.I am still working on getting my system to communicate fully so I'm not an expert. But. The addressing scheme for the batteries is kind of important for any functionality at all. If the addresses are wrong, nothing works, and you will get error 60 and 61 on eg4 inverters. Solar Assistant reads the batteries in order, and therefore also relies on addressing. EG4 addressing is odd to me, but the scheme is easy.
up is on, down is off. add the digits together to create an address. Example below.
switches are read from right to left. (8,4,2,1)
Address 1 = down down down up
Address 2 = down down up down
Address 3 = down down up up
Address 4 - down up down down ...
Disconnect all the data cables.
Now you just have four batteries hooked to a common bus bar and your inverters hook to the same common bus bar.
Now let physics take over. You know, electrons flowing.
Wire each of the six devices independently direct to the Raspberry Pi that hosts solar assistant.
You will probably need a $20 common USB hub to accomplish this.
You can change the addressing in solar assistant by moving USB cables on the hub.
The point I was trying to make is that you either use the eg4 communication scheme OR use the solar assistant monitoring scheme.
I still don't understand the benefit of having the batteries and the inverters "communicate".
It seems based on all the discussions in this forum to be more trouble than it's worth.