Yes, the right one is what I would like to do.Is the right hand illustration essentially what you are imagining? Or are you talking about a situation where there would be no battery, or a situation where the fuse block would be wired to the SCC's load output?
View attachment 82862
The solar charge controller can be connected to a branch circuit if its under 24 amps.Don't you need the fuse on the output terminal of the SCC if you have short circuit down the line?
and fuse at the battery terminal?
Without the fuse to protect the two wires from SCC if the ends of the wires that go to the bus bar on the fuse block shorted together?The solar charge controller can be connected to a branch circuit if its under 24 amps.
Or 2 branches for 48 amps.
The branch circuits are fused.Without the fuse to protect the two wires from SCC if the ends of the wires that go to the bus bar on the fuse block shorted together?
legend {
{} { functional block }
nnn|NNN| { fused busbar position where nnn is the wire guage and NNN is the fuse rating in amps }
nnn|UUU| { un-fused busbar position where nnn is the wire guage }
<-> { bi-directional current flow }
-> { uni-directional current flow }
<- { uni-directional current flow }
}
fuse_block {
positive {
feeder {
006|UUU|<->100A_fuse<->battery.positive
}
branches {
010|030|->inverter.positive
010|030|->inverter.positive
010|030|<-solar_charge_controller.positive
010|030|<-solar_charge_controller.positive
}
}
negative {
feeder {
006|UUU|<->battery.negative
}
branches {
010|UUU|<-inverter.negative
010|UUU|<-inverter.negative
010|UUU|->solar_charge_controller.negative
010|UUU|->solar_charge_controller.negative
}
}
}
10 awg wire with 105c insulation is rated for 60 amps in open air.I know that the branch circuits are fused for each branch to protect each branch, but you have two wires from SCC that are connected to the positive and negative bus bars of the fuse block, so what is protecting the SCC wires if those two wires of SCC shorted together?
The battery is connected by a single pair of wires to the feeders and is fused as close as possible to the battery positive.Same for the battery since the two battery wires are also connected to the bus bars.
Why would you want
Lol. I'm good. Thanks for all the info. Much appreciated.@Debbies my apologies if your eyes have glazed over.
That’s the only possible practical issue!like to be powered by a battery at all times.... don't forget to disconnect the panels before battery service.
like in my setup: I have <6” between SCC and 63A breaker, unfused 6ga. There’s a fuse in SCC- the short 6ga wires aren’t really unprotected. At some point you have to get power someplacebattery is connected by a single pair of wires to the feeders and is fused as close as possible to the battery positive.
I'm not really seeing the problem
No. The wire or cable from the SCC should be of the right awg to carry all the current from the cc. That cable can not handle all the current from the battery. The circuit between the SCC and battery must be fused at the battery end. The SCC is considered a Limited Supply. The battery is not a Limited Supply.Don't you need the fuse on the output terminal of the SCC if you have short circuit down the line?
and fuse at the battery terminal?
Yes and if connected to a fuse block branch connection, the fuse to protect the wire from battery power is already in place.No. The wire or cable from the SCC should be of the right awg to carry all the current from the cc. That cable can not handle all the current from the battery. The circuit between the SCC and battery must be fused at the battery end. The SCC is considered a Limited Supply. The battery is not a Limited Supply.