SOROTEC REVO II 5.5k No pv displayed on display

Mik

New Member
Joined
Mar 17, 2021
Messages
10
Hi I have just installed one of these units and app output cloudy is around 160-170 volts, voc of around 180 from the 5 panels x 2 into 1 parallel, 36 volt panels but nothing is displayed as in from solar array. I measured the voltage on the input at the pv input so where is the voltage going???
batteries connected and charging from mains.

when I don’t put mains on and switch the unit on, the unit powers up, not charging batteries also no display of pv on display.

this if off/on grid unit so a little boggling at moment.
 
Shall I try a single array of all 10 panels giving me 360v and 7 amps?
 
Last edited:
List your setup in the menus of the inverter. I don't know that unit.
Also link specs.
 
List your setup in the menus of the inverter. I don't know that unit.
Also link specs.

not changed anything in the menu as yet, want to make sure it was working first

I have the 5.5k unit, its operating voltage is anything above 120 VDC so why nothing in pv display

MODELREVO II 3K-24REVO II 3.2K-48 REVO II 5.5K-48
Max PV Array Power4500W
Rated Output Power3000W3200W 5500W
Maximum PV Array Open Circuit Voltage500VDC
MPPT Range @ Operating Voltage120-450VDC

put a red cross where the PV is supposed to be providing power
1655710935104.png
 
Yeah, no need to connect the panels in a series/parallel mix.
Make one string with all panels in series. That way you will also ensure good production through the afternoon.
Remember the minimum activation volt is just a threshold to awaken the system.
As long as you stay under the max PV level you're good.
 