New Member
I have 20 450w Helios Plus EGE-450W-144M (M6) panels, that's supposed to be a 9kw system but even on sunny no cloud days I get a max of 4.8-5kw at a time, if there is a bit of clouds it goes down to 1-2kw. Is this normal?
Its integrated with the inverter. Its a victor max 10.2kw, here are the specs in a pic. I think max voltage was 500VDC and 1MPPT for a max of 27AmpsTilt will be important. From the pics the tilt looks pretty flat, even for your location. That being said, I don't think the tilt is a significant factor, right now anyway, since we're at the solstice. It probably will be in the winter though.
What type of charge controller do you have (mppt or not)?
Well according to the manual and what I set up, max charging current in the inverter is 100AWhat are your AIO's settings for PV charge current and max charge current?
Hmnn... Could be a setting on your inverter to limit the export? I did some off grid work in Puerto Rico after Maria but no grid tie so I'm not familiar with thier grid interconnection rules.Currently my load is around 5-6kw and solar max output doesn't go past 5kw
Edit: with or without load I never seen it past 5kw when charging battery or house load exceeding 5-6kw.
100a at 56 volts = 5.6kwWell according to the manual and what I set up, max charging current in the inverter is 100A
In this case if I up the setting to 120A or even 160A (max setting)100a at 56 volts = 5.6kw