I have an existing RV mounted Lifepo4 system that I'm trying to integrate a new Ecoflow Delta Pro + extra battery into.
The current system has 420Ah at 14v connected to 2 inverters. It also has two individual arrays, each going through its own MPPT controller (Outback FlexMax 60) to charge the LP4 bank.
- One array is always active and consists of a series string of five 165W, Imp 9A, Vmp 18.22v, Isc 9.61A, Voc 22.32v panels.
- The other array is only 4 of the same panels and active only when parked and deployed at a campground.
Because of the charge controllers, BOTH arrays always put out 14.4V at whatever amps they can pull from the available light. So I can connect them in parallel to the LP4 BMS and all is well.
- The head scratcher -
The EF DP only has a single solar input port and only draws a max of 15A.
Ok, Fine, I'll sacrifice a few amps (18A-15A = 3A waste?) if I were to just bypass the MPPTs and wire both arrays in parallel directly into the DP solar port.
BUT, how will the DP react to having two arrays connected in parallel to the same port, each with differing voltages? Typically, the 5-panel array is at about 80v and the 4-panel array at 68v.
Will the 80v array drop to 68v? Won't that strain one array or the other?
Changing either array to match the number of panels in both would be a major PITA and is a dead last resort.
I can't run the arrays through the FlexMax CCs and feed the same V to the DP, because they're powered by the batteries they normally would charge and the DP solar input port won't be providing that.
Thoughts?
Thanks!
The current system has 420Ah at 14v connected to 2 inverters. It also has two individual arrays, each going through its own MPPT controller (Outback FlexMax 60) to charge the LP4 bank.
- One array is always active and consists of a series string of five 165W, Imp 9A, Vmp 18.22v, Isc 9.61A, Voc 22.32v panels.
- The other array is only 4 of the same panels and active only when parked and deployed at a campground.
Because of the charge controllers, BOTH arrays always put out 14.4V at whatever amps they can pull from the available light. So I can connect them in parallel to the LP4 BMS and all is well.
- The head scratcher -
The EF DP only has a single solar input port and only draws a max of 15A.
Ok, Fine, I'll sacrifice a few amps (18A-15A = 3A waste?) if I were to just bypass the MPPTs and wire both arrays in parallel directly into the DP solar port.
BUT, how will the DP react to having two arrays connected in parallel to the same port, each with differing voltages? Typically, the 5-panel array is at about 80v and the 4-panel array at 68v.
Will the 80v array drop to 68v? Won't that strain one array or the other?
Changing either array to match the number of panels in both would be a major PITA and is a dead last resort.
I can't run the arrays through the FlexMax CCs and feed the same V to the DP, because they're powered by the batteries they normally would charge and the DP solar input port won't be providing that.
Thoughts?