Hi all quick question
I have just installed a second 150/70 victron smartsolar MPPT to my 48v system with 2 new panels facing south
Array 1 has 6x425w panels 2s3p
Array 2 has 2x425w panel 2s
They are both on the exact same charge settings and linked to eachother and to my bmv-712 shunt with VE. Networking
Agm batteries at 90%soc , one mppt is showing absorption and 2000w , the other is in float with 0w
If I isolate the big array (1) , then the little new one drops off float onto absorption and then reads over 700w
Is this all normal ? I thought once linked they would be in the same charge state and carry the load equally , has something gone wrong ? am I losing power ?