Victron Quattro II won't charge.

SteveDeFacto

New Member
Joined
May 16, 2022
Messages
28
I finally got my Quattro II from Current Connected a couple days ago after a seller on Amazon kept sending me MultiPlus units which I had to return over and over, over a period of months. I mainly bought this Quattro II for its dual AC inputs so I can charge batteries from grid and generator at the same time.

This morning I woke up early and I needed more power. I thought I could just screw in an ac plug and start charging. This initially appeared to work flawlessly. About 30 minutes later, I started hearing a repeated clicking sound and realized it had stopped charging.

I realized that I didn't properly secure one of the wires and fixed that, but now when I try to connect AC to either input, I just hear this clicking sound periodically even after fixing the lose connection?
 
Do you have any LEDs flashing while it is clicking?

Also, yes the Quattro has 2 inputs, but it automatically selects power from the active input. If both inputs have power it defaults to input 1.
 
Do you have any LEDs flashing while it is clicking?

Also, yes the Quattro has 2 inputs, but it automatically selects power from the active input. If both inputs have power it defaults to input 1.
The charging led flashes for like a split second when the relay clicks. No errors or faults shown in UI.

It's almost like there is a short or something because the power draw surges when the relay clicks. It keeps popping the breaker on my 200 foot extension cord I ran from the house.

I got tired of running back to the house to reset breaker so I also tried creating a loop for debugging by feeding the AC output to the AC input and it gets past the surge without popping but still doesn't charge. I fiddled with several settings including current limits but even with a 9.5a limit, the issue persistents and house fuse still pops.
 
Do you have any LEDs flashing while it is clicking?

Also, yes the Quattro has 2 inputs, but it automatically selects power from the active input. If both inputs have power it defaults to input 1.
Ok so I somehow managed to get it to stop immediately popping the breaker after fiddling with settings in VEConfig. Now it just pops the breaker after 5 minutes again.

I turned charge current down to 10a, input current down to 5a, turned off ground relay, turned off virtual switch, and I turned off power assist. Still pops breaker in 5 minutes. I am able to run a 12k btu AC off this extension cord without issue... I don't know what else to try?
 
Do you have any LEDs flashing while it is clicking?

Also, yes the Quattro has 2 inputs, but it automatically selects power from the active input. If both inputs have power it defaults to input 1.
Ok, I figured it out. Saw a wiring diagram of the Quattro-II and realized the input 1 and output 1 are connected.

So my entire house load was being pumped through this 200 foot extension cord plugged into a 15a outlet. I switched to input 2, set some reasonable limits, and now it's working flawlessly!
 
Last edited:
So normally your Quattro 2 is only charged from solar? And then you temp hooked up an extension cord to AC in 1 to charge it?
 
So normally your Quattro 2 is only charged from solar? And then you temp hooked up an extension cord to AC in 1 to charge it?
Usual setup was solar during the day and power supply/iCharger/extension cord at night. The Quattro 2 is new.
 