15A * 120V = 150A
Get some beefy wires.
Explain this new math to me, I’m quite intrigued ?
15A * 120V = 150A
Get some beefy wires.
Explain this new math to me, I’m quite intrigued ?
Voc can be 15% higher or more in really cold conditions. Most panels have a Voc temperature coefficient around -0.3%/ºC. So it only takes a 6ºC drop in temp to increase the Voc 2%. Just getting to freezing will be 7%-8% increase for most panels.You need to calculate worst-case Voc at the coldest temps your panels will ever see (at night). At least a 1-2% increase is typical
Clarifications:
Wood working tools will be used 1-at-a-time. This is a hobby shop, nothing more.
12 inch DeWalt compound saw draws 15amp, compressor is likewise small, 12 amp I recall.
So I will use a surge clamp to determine an appropriate inverter. TBD.
I have two LiFePO₄ batteries in series. They have been in series most of this year. I do not have any sort of balancer. They have stayed in balance just fine. The trick is to first charge the two batteries together in parallel and let them settle in parallel so they start life at the exact same SOC. Then you can put them in series. I know they are still in balance because my battery monitor is setup to monitor the voltage of both. Both batteries are at the same voltage to the nearest 1/100th of a volt, according to the battery monitor.My immediate quandary involves a battery balancer for lithiums in series.
Ten years. Yeah, the Morningstar's are solid as a tank. No moving parts to fail. Silent. Programmable, networked.60 amp Outback or 60 amp Morningstar. Would not seem to need 80. I only read about problems with EPever.
I have the Morningstar running 10 years no issues, very programmable.