I don't know if it has a place to ground the case, but if it has one I will connect it. (It is still on the way here so I don't have it yet)The metal case of the transformer should be grounded
Thank you for confirming this. This has been my greatest fear of getting wrong. I thought for a while that I might bond G&N in the combiner box but that would mess up my SPD, so the service panel was all that was left.Yes, the breaker box is an ok place for the N-G bond
I've intentionally chosen components that will permit me to add more panels. I will leave a pull string in the conduit for future PV strings. I just want to know how much I'm going to generate from the 4 I have so that I will know - for sure - how many I need for future plans.What is the purpose of the combiner box?
I will have to look into this because I hadn't heard about it before. I thought that the DC breakers are made to suppress the arc when they trip?If you want to be to code you will need arc fault protection and that is sometimes built into combiner boxes.
I don't want to feel anxiety over the safety of the system. It will be accessible to my grade-school-aged children, so I need it to be safe but not necessarily up to code. They are old enough that I can tell them what not to touch and they will listen.but I guess you aren't going for code compliance because growatt is not code compliant
Everything? I would think that it would protect the transformer from a misbehaving inverter, but how does the breaker on the output of the growatt protect everything?Double pole breaker on the output of the growatt, will protect everything in the event of a problem
I'm super-curious to hear more about this? The breaker on the positive terminal of the battery lead was suggested by Signature Solar. This is worth investigating, imo.No breakers on battery leads, the EG4 already has those.
Please forgive my clear lack of understanding - I'm only 3 months into learning about all of this. I believe that my transformer is already connected to the breaker box via the double pole breaker? You clearly mean for me to connect it to the breaker box in some other way, but I don't know how you mean?Actually move the transformer connection to the breaker box
If I put a double pole 25A breaker in between the growatt and the transformer... would I not need to purchase a wholly new service panel for that one breaker?and use your 25A breaker to input from the growatt,
Wonder why you are using a combiner box? Future extension? For 4 panels in series a box is not needed.
Why did you choose the SPF 5000 ES over the 6000T DVM (which already got Split phase)?
5000 ES = $900 + Split phase transformer $350 = $1250 +wiring and labor.
6000T DVM = $1100-1200
I don't know - with the 6000T and the MPP 6kw products available I don't really see a reason anymore to mess with a Transformer.
I think that's what I have done, right? The "main service panel" is the siemens main lug panel in my diagram. It just feels weird to bond it there because it's "downstream" from my whole solar system. Meaning, the combiner box --> inverter --> transformer --> service panel.Usually ground and neutral are bonded at the main service panel. But I would assume that the autotransfomer or inverter also bonds those. Look up the manual and measure!! if you got bonds somewhere else. I think part of the controversy was that screw that bonds ground and neutral in the 5000 ES. Measure all your devices before you connect them. So you know.
I would definitely breaker the output of inverter. Transformers have a tendency to burn up. Short out. Breaker will trip. Replace transformer. The current configuration. Transformer shorts overloading inverter. Now replacing both.
Signature Solar is usually good about that.Because I purchased the inverter directly from Signature Solar, I can assume that the screw is not present and that ground and neutral are not bonded in the inverter.
When I commented I wasn't sure if you already had the components purchased.This is my first attempt at DIY off-grid solar, so it's possible that I chose the wrong inverter. I picked the SPF 5k ES because of its higher PV input voltage, which I thought would make my PV array configuration a lot easier since I can put up to 6 of my chosen solar panels in series. If I were doing it all over again, I would probably not have gone this route.
Actually are you still planning to run 240v appliances ? If not return the transformer.