Ok... thanks for the help. I have an amp clamp, but when the clamp read less than 1 amp on my 4000 watt array I was suspect and used the probs. And of course now there is no sun so not much I can do now...
Ok, then something weird is going on? How many panels in how many strings do you have? Do you have strings of three panels that are supposed to be putting out 96V? There could be some kind of fault that "confused" the electronics. The very first thing I would suggest is doing a full shut-down, which would include disconnecting the battery connection.
Here's what I would do. Tomorrow morning, start by switching off the main AC-to-house breaker, then switch off the solar breakers (are there breakers?), then switch off the inverter, then disconnect the battery terminal to the inverter, so the unit is totally without power.
After a minute or two, reconnect ONLY the battery to the unit. You may need a resistor (lightbulb) in line for bringing your capacitors up. After the battery is connected, press the "ON" button and power up the unit. If it boots correctly and displays the battery voltage, flip the solar breakers back on one by one. Check as you close the breakers whether or not the amps coming into the system is going up. If you see the amperage going up, then the system just crashed in some way and needed a reboot.
If you do not see amperage increasing, you need to check each solar string for bad connections, and/or wire breaks. Does everything look clean, or are terminals corroded?
Once you think everything is OK, you an flip the main AC breaker back on to send power to the home. You might want to unplug as many things in the home as you can so the startup surge is not too high.
Good Luck!