Charger comes on Wednesday 6/3/20Do you have any way yo charge your batteries? AGM batteries should not be left discharged for long periods and 3 years is a lot, also be careful not to overcharge them.
Charger comes on Wednesday 6/3/20Do you have any way yo charge your batteries? AGM batteries should not be left discharged for long periods and 3 years is a lot, also be careful not to overcharge them.
After 3 years there will either be a loss of capacity or the AGM batteries will be dead.How long does an AGM hold it's initial charge from the factory? I have had 3 of them in the shipping boxes for almost 3 years. I hope they haven't discharged too much. They've been in my storage unit through all the seasons here in Maine.
I've never been close to rich/well off/middle class etc. But I am resourceful. Because I have dedication to learning about the things I need. It doesn't take much work to find info on how to care for your equipment (even while being stored) and a motivating factor might be the inability to replace your hard earned investment.I hope I don't have to trash them. I can't afford more. It took me 3 years to get the six I have now. I didn't want to start a system with only 3 100aH AGM batteries. I know it would be useless for what I need. So, reading that you can't add on to an existing bank on a system, I decided to wait till I could afford more batteries. Now?...ya well now. Starting to look like poor people aren't entitled to go off the grid.
SCC, is solar charge controller.I don't understand SSC, and aren't there ways to revive a dead lead acid?
The idea of an equal battery Bank is all cells of same age and type, because what's known as internal resistance (IR) needs to be as close as possible. This is so the batteries in the bank charge and discharge at the same rate. Very important.These are the batteries I bought. 3 are fresh and 3 haven't been charged since factory 3 years ago.
hey, I got my volt meter and the one old battery I have at home reads 12.5v while the newer ones all read between 12.8v and 12.9v. How much damage would the three old batteries do to the new ones if I use them anyway? I'm really not feeling good about buying three more batteries at $179 a pop. Oh....and I haven't charged anything yet. I got an AGM charger that plugs into 110v. That's my next step.The idea of an equal battery Bank is all cells of same age and type, because what's known as internal resistance (IR) needs to be as close as possible. This is so the batteries in the bank charge and discharge at the same rate. Very important.
Tbh, if you've invested in 3 new ones, they really need matching to 3 more new ones because the ones in storage definitely wont match and the outcome will be a very short battery life time and wasted investment.
Sorry if I sound negative, I don't mean to come across like that..
So I got my volt meter and agm smart charger in today. The one old battery I have at home (other two are in storage unit) reads 12.5v. I just put it on the smart charger to top it off. I really wish I would have done more research in the beginning.There is a lot of info on AGM shelf life online:
Re: Shelf life of lead acid deep cycle batteries
Post Sun Apr 22, 2018 5:31 pm
Most AGM deep cycle batteries have about a 3%/month self-discharge rate when stored at room temperature. Lower temp = lower discharge. Higher temp = higher discharge. After 3 years, its as pretty good bet they are fully discharged. Holding them in a discharged state will result in capacity loss. How much depends on several factors, including the chemical makeup of the battery. With sealed AGM batteries, the loss can be less than flooded lead acid.
Use a voltmeter to measure each battery. They are likely to read 0 volts, but note each one.
Next, try to recharge them with a quality "smart" charger driven from a generator or other steady AC source. If the charger won't start charging because the battery voltage is too low, connect a good 12V battery in parallel to the dead cells and charge until there is a measurable voltage on them, then disconnect the 12V auxiliary battery and proceed with charging until complete. Once a set is complete, set aside and charge the next set. Let all the charged cells rest for 24 hours.
Measure, and note, the voltage of each. A fully charged battery will measure around 12.8V.
If all take a charge, you can try to get an estimate of the battery capacity by running a discharge test.