diy solar

diy solar

Which connection on lv5048?

D. Abineri

New Member
Joined
Jun 25, 2021
Messages
306
Location
Blacksburg, VA
The manual says "Before making AC input/output connection, be sure to open DC protector or disconnector first. " when discussing making the AC connections.

In this instruction, are they referring to the PV DC connection or the battery DC connection that should be disconnected?

Thanks
 
In my opinion, they are meaning the Battery Connection, as in for safety, in case the inverter section is turned on you won't get zapped when connecting your AC output. See on Page 5 of the manual, they refer to a DC protector:

"
Battery Connection
CAUTION: For safety operation and regulation compliance, it’s requested to install a separate DC over-current protector or disconnect the device between battery and inverter. It may not be necessary to disconnect the device for some applications, however, it’s requested to have over-current protection installed. Please refer to the typical amperage in the table below as required fuse or size of the breaker.
"

I would also disconnect PV solar input (at the combiner box disconnect, or wherever), as a safety precaution for while you're making the AC connections, since PV input could power the inverter (if the inverter supports batteryless operation).

Of course it goes without saying, to also make sure the grid power incoming circuit is not live when making the AC input connection. Just a little common sense (and a voltmeter to check) and make sure there is no surprise power anywhere while you're fastening the connections.
 