Hey all. I was tilting my panels today (I made mounts last year that allow me to rotate to proper angle) and forgot to disconnect my main PV breaker before I started. When I came in the PV 1 input was no longer working on the LV5048. I noticed the breaker was on and switched it off and back on. The LV5048 shows the PV connections, clicked on and then clicked back off. The breaker is 50A 150VDC. I switched the breaker off and went outside to test voltage at my combiner box. It was 151V!
At the PV input by my LV5048 right now I am seeing ~80V with the breaker turned off (measuring positive before the breaker and the negative line). When I turn on the breaker, voltage drops to around 50V. I can turn on the breaker and the LV5048 will show PV connection, click on and then click back off after a few seconds. The PV1 display shows ~55V for a few seconds after it clicks on and back off.
Did I blow the breaker? I thought the breaker was supposed to trip? I am at a loss of where to go next. All PV inputs at the combiner box are now measuring around 100V. I am not sure why I was getting a reading of 150V earlier, but I am positive that is the voltage that was coming through every combiner box input, and that measurement lasted for several hours.
Sun flare? Should I rewire my panels to the the VOC down to ~80V from ~100V - ~120V? The LV5048 has a max VOC of ~145V, and now I am feeling nervous. I have been running this setup for 18 months now without a problem, but this is the first time all 18 panels were properly tilted.
Could a ground fault somewhere on the panels be causing the issue? When I tilted one of the wire inputs to the back of a panel got pulled, but I removed the cover and everything looks ok. None of the PV lines seem to be damaged anywhere.
EDIT: The breaker I am using between the PV input and LV5048 says max volts is 125, trip amps are 65. I am guessing the 150 volts damaged something in the breaker.
At the PV input by my LV5048 right now I am seeing ~80V with the breaker turned off (measuring positive before the breaker and the negative line). When I turn on the breaker, voltage drops to around 50V. I can turn on the breaker and the LV5048 will show PV connection, click on and then click back off after a few seconds. The PV1 display shows ~55V for a few seconds after it clicks on and back off.
Did I blow the breaker? I thought the breaker was supposed to trip? I am at a loss of where to go next. All PV inputs at the combiner box are now measuring around 100V. I am not sure why I was getting a reading of 150V earlier, but I am positive that is the voltage that was coming through every combiner box input, and that measurement lasted for several hours.
Sun flare? Should I rewire my panels to the the VOC down to ~80V from ~100V - ~120V? The LV5048 has a max VOC of ~145V, and now I am feeling nervous. I have been running this setup for 18 months now without a problem, but this is the first time all 18 panels were properly tilted.
Could a ground fault somewhere on the panels be causing the issue? When I tilted one of the wire inputs to the back of a panel got pulled, but I removed the cover and everything looks ok. None of the PV lines seem to be damaged anywhere.
EDIT: The breaker I am using between the PV input and LV5048 says max volts is 125, trip amps are 65. I am guessing the 150 volts damaged something in the breaker.