I was speaking about high voltage …and why I don’t use it…that’s all …The thread is about HIGH VOLTAGE and reasons why to fear it...
Not how to use low voltage for random reasons...
Please stay on topic.
![Thumbs up :thumbsup: 👍](https://cdn.jsdelivr.net/joypixels/assets/8.0/png/unicode/64/1f44d.png)
I don't know enough about electronics/MOSFETs and other parts to understand why. But I've just been told that the MOSFETs are typically only rated to 60v, so series connecting them makes them prone to failure very quickly.
I will say, it would be awesome to be able to just series connected a 6x Rack of Server Rack batteries, to make a 307.2v nominal Battery to connect to a SolArk 30k or 60k. Easy peasy.
Who's gonna try it first???
Need a BMS for HV Batteries and an HV inverter.Well, I guess this thread has confirmed what I expected. Based on likes and positive posts, vs negative. Seems like it's about 50/50 in terms of people that understand HV batteries aren't that different than HV PV and HV AC.
And yet for the half of people that do seem to be afraid of HV batteries, but at the same time not HV AC or PV, I haven't seen a convincing argument for why they think it different.
It's interesting that some folks think HV batteries need more safety systems built into the technology before it's acceptable to adopt, while at the same time they have a 240V AC power panel in the house that'll kill you just as easily if you don't follow the appropriate safety precautions. HV DC batteries should be treated exactly the same way. Follow the appropriate safety precautions, engineer the system appropriately, and it'll serve its purpose well. I guess it's just that case that people will be afraid of what they don't understand.
The forum is a great place to discuss battery voltages and options.In the topic are more people who replay on it to stay on low volt
I only tell that you do not need high volt its a option.
And yes high volt speciaal if you go up to 120/230 voor dc is more easy to set to ac 120/230volt.
This is how Solar panels work if it go to a grid network.
But that is not something you gone beult your self easy on a diy project
Reason is al ready tolt about it .
Its dangerous to do on diy .
And not even tolt about you insurance that will not pay out of it go wrong .
And even if it go wrong it means real wrong.
So its a good thing to tel that are other options to use.
That is a reason i have told this that are other options.
Its a forum to talk about it or not ?
Soon a natural resource will be degraded EV batteries in the 350-400 volt range, however there is no easy method to utilize. Producing HV inverters will be an expensive proposition.
Would it be easier [and safer] to make a charge controller with 350-400V input and 48V output? Will power a smaller 48V battery bank with plenty of inverters to choose from.
You can do this now by using the 12V accessory battery with boost controller for 48V, but you are limited with amps.
Of course it’s important to realize that “HV batteries “ mean different things to different people. There are a number of different varieties to consider, I’ll describe two, I’d be interested if others can describe other design styles:I find it interesting that people are scared of HV batteries.
All the batteries in that video are parallel...Have any of you considered the DC arc on HV DC batteries, and what it takes to extinguish that arc??
PV has a very limited available fault current as compared to batteries! Especially Lithium batteries! The reason that they can be charged at way higher rates than lead acid batteries is the same reason that they can also produce way higher output currents than lead acid batteries! (When compared AH/AH)
Plus PV is generally not stringed at more than 2P. Usually the second string in parallel brings the available fault current up to the short circuit current rating. So you really shouldn't have more than 2 strings in parallel.
Example:
(12) HT 450w Bi-facial solar panels, stringed 6S2P, would give you 246.6Vmpp and a SCC of around 22Adc (plus a few amps from backside, if you wish). Total wattage rating of 5,400w. (Again, plus a little bit from backside, if you wish.)
A 5kWh battery at "48V" nominal (51.2V actual) could easily do a discharge of 100Adc (I'm referring to what the cells could handle, at least for short periods.) Short circuit current would be magnitudes higher!
A 5kWh battery at 400Vdc would be 12.5AH. Therefore going off of the same 1C discharge that I used for the 48V battery, this theoretical battery could easily push 12.5A for quite a while. HOWEVER, if you were to short circuit this 400V battery, you would get MUCH HIGHER amperage!! Plus, the voltage wouldn't dop to zero like it does with a PV short circuit!
What if we were talking about 30-60kWh of high voltage DC battery? Because really, that is where the high voltage battery argument shines, right? We would be talking 75-150AH.... Anybody wanna mess with 500-1,000Amps of fault current at 400Vdc??
My biggest point here is that when you have a short circuit on PV, the total power flowing drops off, and your voltage drops off as well. But you still get a pretty decent arc! But when you short circuit a battery (especially a lithium battery) your total power flow GOES UP!! And the voltage drops only minimally! I do realize that once you pull an arc from a breaker or other contact opening, the voltage rises up again. But PV is waaayyyy less potent in a short circuit condition than a battery!!
Another thing that factors into the whole debate around DC vs AC being "worse" at a given voltage is the fact that DC is a continuous current, where AC is not. AC is hitting zero amps 60 times each second (or 50 times, depending on where you live). That zero point every 17ms gives much more chance for an arc to get extinguished!
Anyone every done a short circuit test on solar panels at >100Vdc? That's a pretty serious arc! I did it just recently with ~120Vdc and ~20A short circuit current! Anyone care to try a short circuit test on a battery that is >100Vdc? If someone is brave enough to do this, please video it and show us the results!
By the way, here is a YouTube video by StyroPyro that shows some pretty serious DC arcing!![]()
I don't think he runs very high voltage in that video unfortunately.... I couldn't remember from when I had watched it before, but just skimming through looks like maybe ~60-72Vdc or so. (5S or 6S at 12V??) (Though I don't think much higher voltage would be very safe, to be honest.)
So anyway.... Are any of you guys that are saying high voltage batteries aren't inherently more dangerous than high voltage PV up for the challenge??
I just posted a video of the Kiruna K1050E
It had two stacks of NiCad batteries in it and I got a hell of a lot of shocks.\
I believe it was 220 volts..
But the inverters (at least SBS, which I have) support various firmware update versions depending on which battery, e.g. I can only update to a certain version using LG RESU-10H; later firmware isn't backwards compatible.
Example:
All else being equal, I'm happy to work with HV. With HV AC, I can turn off the circuit, and work safely.Well, I guess this thread has confirmed what I expected. Based on likes and positive posts, vs negative. Seems like it's about 50/50 in terms of people that understand HV batteries aren't that different than HV PV and HV AC.
With diy batteries, it gets to a point where you are working with live wires. Can't turn it off when connecting all the cells together. 500v is different from 50v.
There is more expertise out there that you can avail of on 240VAC, from all the electrical DIY and electrician forums. I'm pretty sure with 3 months of forum reading, I can get farther with self education on 240VAC, than 240VDC battery systems.
I am less afraid of 600VDC solar strings than 600VDC battery systems because there's existence proof that people aren't killing themselves left and right with their solar strings, despite minimal safety education. There aren't enough datapoints for battery systems and I don't want to be an early adopter.
For VDC, I don't know yet where to get the training on that -- do I have to be a EV tech or something? What's the flashover risk and do I need special PPE? What safeties are taken care of by the traction battery BMS / module BMS, and which ones do I still need to know about? Maybe I just need to go on the right forums to get the appropriate certifications.
IMO the early adoption drivers are
There could be some fundamental blockers like ready-to-go modules having extra mandatory safety. For instance you have to have the right $$ tools to be able to unlock a traction battery that throws a code. Things above 100VDC have extra NEC / UL requirements on how they are designed.
- Availability of cheap equipment
- Accessibility of building hardware from scratch (I don't think very many people in the world are going to be able to build high voltage DC circuits from scratch)
- Education on safe practices (and this is hampered because unlike 240VAC you don't have a 120 year old profession of being an electrician that has built up a corpus of learning material. It'll take a long time for this to bootstrap on YouTube and forums)
- Intro classes in university and community college do not work at these DC voltage levels. So you don't have EZ mode onboarding. While trade school has plenty of people working at 240VAC right away.
- I bet the natural inclination of a lot of trade school and university educators would be, "No thank you", if posed the question of how to bootstrap this expertise in DIY community. So it'll be up to some adventurous individual innovators.
The Sunny Boy Smart Energy products actually look fairly interesting as an all-in-one HV DC Hybrid Inverter, and the prices for the models they have out seems fairly good with most of the one out being less than $2k. But I wouldn't be willing to jump back on their stuff if they don't shape up their act with firmware and supporting different battery protocols more openly.
The thumbnail is clearly 5S. Which would put it at (5x12V) 60 volts.All the batteries in that video are parallel...
12V... MASSIVE current potential.
First of all, this video looks to be ~60V, not 12, 24 or 48V. (See my marked up screenshot of his thumbnail above.) And second, I was not using that video "as an argument against HV battery systems". I had just used that to illustrate arc capability of batteries in general.Hmmm, you post of video of a low voltage battery system with massive cables, just like folks are doing with LV battery systems, as an argument against HV battery systems.
Any fuse on a HV battery needs to be rated to withstand the arc from the high voltage while opening up under fault current. The higher the voltage, the further the arc will reach!Even if you didn't install a 25 or 30 amp fuse near the batteries, which you should because that's more than the current you'll ever need, the 10 gauge wires used to connect a HV battery to the inverter would burn up and act like a fuse and instantly open up.
That is not a true comment.... A quick Google search tells me that the Tesla Model S's motors take up to a combined total of 615kW (for 825 bhp) and the battery is 375Vdc. That comes out to (615,000 watts/375Vdc) 1,640 amps!! And that is not short circuit current!The battery system in that video is capable of more than tens of thousands of amps. No HV battery is capable of anywhere close to those kinds of currents.
HV will arc waayyy sooner than LV! That in itself deems it more dangerous!I made this exact point earlier in the thread, HV battery systems just aren't capable of carrying the kinds of currents that LV battery systems can. So, for a lot of scenarios, there is less risk of accidents having to do with high currents.
Where are you getting your 50 amps number??? #10 copper is definitely not NEC rated to 50 amps....... And if you are saying it won't carry more than 50 amps because of resistance, etc., then I challenge you to try doing a dead short on even a 6V battery using #10 and put a clamp meter on there! You will have much much more than 50A!10 Ga wire can only carry about 50 amps and that kind of current range is possible in a PV or a Battery system. So really not much practical difference.
Nope. Good (silicon) ones go to 200V, and you can get them rated to 600V. In fact the most popular MOSFET out there for high power ebikes is the IRFB4110, a 100V/180A MOSFET (so good up to about 72V battery.)I don't know enough about electronics/MOSFETs and other parts to understand why. But I've just been told that the MOSFETs are typically only rated to 60v, so series connecting them makes them prone to failure very quickly.
More than that. The plaid can put out 760kw, and the battery is going to be sagging to ~350 volts at those loads. So that's over 2000 amps.That is not a true comment.... A quick Google search tells me that the Tesla Model S's motors take up to a combined total of 615kW (for 825 bhp) and the battery is 375Vdc. That comes out to (615,000 watts/375Vdc) 1,640 amps!! And that is not short circuit current!
I agree that availability of inverters is the main reason. There are some high voltage BMSs but their heritage is EVs and the have a lot of features not needed for stationary storage so their prices tend to be high. A high voltage DIY battery can be assembled from a string of LFP cells and the cost per kWh should not be higher than the typical DIY battery.there is a lack of inverters, and the inverters available require very expensive batteries.