Hey all. I’ve recently discovered this forum and there are some brilliant people and solutions on here, so I’m hoping someone can help me… my solar installer was useless and didn’t really know what he was doing, so I’m learning all this as I try and figure out the system!
My question is “why are we pulling electricity from the grid when we have plenty of battery capacity”?
From the images below (all taken from the SolaX web interface) you can see that in image 1 we are pulling electricity from the grid overnight, as there is no solar and the batteries are configured to keep 30% SOC in case of a power cut in our area (and we have the EPS module fitted for that - so this is as I would expect.
In image 2, it’s a similar story. It’s later in the day when we start to pull a lot from the grid, and I can only assume that ever if there was 3-6kW of solar being produced, clearly the draw from the house was more and hence needing some from the grid - so again, I think this is what I would expect.
But in image 3, we have over 80% battery capacity, yet still pulling from the grid. Is it because of the low draw/power requirement perhaps and the inverter need more of a pull before the batteries kick in???
If it helps, the bits that will probably be relevant to this question are:
Thank you for any help!
My question is “why are we pulling electricity from the grid when we have plenty of battery capacity”?
From the images below (all taken from the SolaX web interface) you can see that in image 1 we are pulling electricity from the grid overnight, as there is no solar and the batteries are configured to keep 30% SOC in case of a power cut in our area (and we have the EPS module fitted for that - so this is as I would expect.
In image 2, it’s a similar story. It’s later in the day when we start to pull a lot from the grid, and I can only assume that ever if there was 3-6kW of solar being produced, clearly the draw from the house was more and hence needing some from the grid - so again, I think this is what I would expect.
But in image 3, we have over 80% battery capacity, yet still pulling from the grid. Is it because of the low draw/power requirement perhaps and the inverter need more of a pull before the batteries kick in???
If it helps, the bits that will probably be relevant to this question are:
- SolaX X3-Hybrid-G4 (10 kW) inverter (set to “self-use” mode, and with minimum SOC for the batteries set to be 30% in case of power cuts)
- 4 x SolaX batteries (1 x SolaX MC0600 HV10230 V2 (3.1kWh) and 3 x SolaX HV10230 V2 (3.1kWh) = total 12.4kWh
- There is a MyEnergi Eddi in the mix also (for hot water diversion)
- 3-phase power to the house (not sure if it makes a difference)
Thank you for any help!