Also make sure your Grid trickle feed is set to like 10watts.As you can see from the picture, when I get over 5kW of draw, grid kicks in. It's not a hard 5kW, as sometimes the battery will provide around 5500W. I must have something set wrong, but not finding it.
View attachment 200914
Grid trickle is set to 20Also make sure your Grid trickle feed is set to like 10watts.
200 ampsWhat’s your max amps discharge set to?
I don't see a place for accumulated discharge. I have the correct total ah. Under discharge, I have it set to 200 amps.What type of batteries and how many?
Are the correct accumulated discharge value registered under Battery from the main screen menu?
If the load are bigger than the discharge value this is normal.
Are you getting any F56 errors?
If all the above: buy more batteries to cope with the size of your load without using the grid.
But it holds during the draw, not just the surge.Seems to only really kick in for surges. Perhaps you need more available current?
I don't do any grid charge. The restriction is so that it puts all the solar into the batteries at those first 2 times.Charging seems fine. What's the Solark say your max discharge is? (And why not grid charge from 1400-1800?)
I appreciate the help. Was hoping I was just not seeing something set wrong.Well I'm out if ideas, then.