Hi, i have a problem with one cell spiking when charging and dropping much more than the others.
I have a 12v pack of 190ah. I did a top balance to 3.65 and did an "in real life" capacity test aboard my boat which I live in to see how many ah I could get from them. This means that amp out varied between 1a and 40a (brief moments). I set the BMS disconnect to 2.7v per cell and when I had gotten 188ah out of the pack the bms triggered when i used a water pump which does a sudden draw of 10amps, as cell no. 2 made a sudden drop below 2.7v. I could have gotten more out of the pack but decided to stop as cell 2 dipped below 2.7v every time I used more than 10 amps at that point.
I watched the cells closely during the test and noticed that cell no 2 dropped down to about 2.9v every time I used any more than 10 amps. The other 3 hardly noticed the sudden increase in power going out of the battery. Once usage settled back at around 2-3a, cell 2 stabilized but stayed .1-.2v under the others.
The real problem began once I connected the charger (victron ip22 30a) set to 30a, cell 2 spiked almost immediately to 3.4-3-5v while the others stayed together at 3.1-3.2. When I had gotten around 50ah into the pack, the bms disconnected as cell 2 reached 3.65v. I then lowered the charge to 15a (while using 5a = 10a going in) and I got a total of 120ah into the battery before it disconnected again....
So to sum up, cell no 2 spikes to 3.65v immediately when more than 10a is going into the battery, is this fixable or is the cell really bad? After all I did get 188ah out of the pack which is good.
It is worth noting that I used the battery for a while before balancing, and the cells behaved much better then. But after a while the cells started drifting so I figured a top balance would be good.
I appreciate any input here!
I have a 12v pack of 190ah. I did a top balance to 3.65 and did an "in real life" capacity test aboard my boat which I live in to see how many ah I could get from them. This means that amp out varied between 1a and 40a (brief moments). I set the BMS disconnect to 2.7v per cell and when I had gotten 188ah out of the pack the bms triggered when i used a water pump which does a sudden draw of 10amps, as cell no. 2 made a sudden drop below 2.7v. I could have gotten more out of the pack but decided to stop as cell 2 dipped below 2.7v every time I used more than 10 amps at that point.
I watched the cells closely during the test and noticed that cell no 2 dropped down to about 2.9v every time I used any more than 10 amps. The other 3 hardly noticed the sudden increase in power going out of the battery. Once usage settled back at around 2-3a, cell 2 stabilized but stayed .1-.2v under the others.
The real problem began once I connected the charger (victron ip22 30a) set to 30a, cell 2 spiked almost immediately to 3.4-3-5v while the others stayed together at 3.1-3.2. When I had gotten around 50ah into the pack, the bms disconnected as cell 2 reached 3.65v. I then lowered the charge to 15a (while using 5a = 10a going in) and I got a total of 120ah into the battery before it disconnected again....
So to sum up, cell no 2 spikes to 3.65v immediately when more than 10a is going into the battery, is this fixable or is the cell really bad? After all I did get 188ah out of the pack which is good.
It is worth noting that I used the battery for a while before balancing, and the cells behaved much better then. But after a while the cells started drifting so I figured a top balance would be good.
I appreciate any input here!