Manual attached. On page 8 it says:'MMP (Iconica in UK) Hybrid 3000W 24V pure sine wave inverter'
" I would need a 32A AC breaker for the AC input of my system, according to the manual."
Can you provide us the user manual and the spec of the unit?
You are in UK which is 230VAC 50Hz system, so 32A breaker does not sound right for 3000W system.
The recommended spec of AC breaker is 10A
for 1KVA, 20A for 2KVA, 32A for 3KVA/3KVA Plus and 50A for 5KVA.
Hybrid inverter specifications:
- Nominal battery voltage: 24V
- Continuous power output: 3000W / 3000VA
- Surge power: 6000VA
- Output voltage: 230V AC
- Output frequency: 50Hz /60 Hz
- Output waveform: Pure sine wave
- Maximum solar input power: 1500W
- Maximum open circuit solar input voltage: 145V
- Maximum solar charging current: 60A
- MPPT operating voltage range: 30V – 115V
- Maximum mains AC charging current: 60A
- Maximum combined charging current: 120A
- Peak efficiency: 93%
- Operating temperature: -10C to 50C
- Supplied with a PC connection cable and PC software CD
- Terminals for mains power connection
- Size: 44 x 30 x 10 cm
- Weight: 9.5 kg