Would be really grateful if I could get somebody to double check this with me and confirm I've got my calculations correct.
Here is the kit I'm using,
1 X Victron SmartSolar MPPT RS 450/100
20 X TRINASOLAR - SOLAR PANEL 425 Watt 24V
The panels will be mounted on a south facing roof with absolutely no shading.
I'm planning on installing two strings of solar panels.
10 panels per string in parallel.
Victron charge controller
450v 100a
Solar panels each
425 watts
42 volts
Solar panels 10 panels in series
4250 watts 11 amps when hot / 4700 watts 10 amps when cold
420 volts
Max amps when cold = 11
Normal amps when hot = 10
The panels will be 45m from charge controller which I don't think will be a problem at 420volts.
I found a good deal on solar cable which is 4 mm² which I think is more than enough.
Do you think this will be okay?
Have I got my calculations correct?
Here is the kit I'm using,
1 X Victron SmartSolar MPPT RS 450/100
20 X TRINASOLAR - SOLAR PANEL 425 Watt 24V
The panels will be mounted on a south facing roof with absolutely no shading.
I'm planning on installing two strings of solar panels.
10 panels per string in parallel.
Victron charge controller
450v 100a
Solar panels each
425 watts
42 volts
Solar panels 10 panels in series
4250 watts 11 amps when hot / 4700 watts 10 amps when cold
420 volts
Max amps when cold = 11
Normal amps when hot = 10
The panels will be 45m from charge controller which I don't think will be a problem at 420volts.
I found a good deal on solar cable which is 4 mm² which I think is more than enough.
Do you think this will be okay?
Have I got my calculations correct?