AC input is wired in. On ac bypass the neutral and ground are unbonded. In battery mode they are bonded, so I lifted that bond per the instructions from Reliance and NEC. The inverter neutral goes to the reliance panel which is just a pass though to the main buss bar. I can put the screw back in...
Since it is grid connected is there another way this is handling the neutral ground bond that is not documented? They really need to send proper electrical schematics with these Taiwanese inverters. Guessing is dangerous.
Yes they were on. I am beyond intrigued to see inside this box. How is DC charging voltage from the mppt input which has the battery disconnected when I was testing (so the output was 100% from solar) so much better!? Granted the lights still flickered but that is at least a halfway decent...
That's correct. It is simply a pass though to the main panel. The neutral ground bond screw in the inverter was removed since I am using a generator transfer panel and not a true sub panel. The neutral and grnd are already bonded on the house side whether the inverter is in bypass or battery mode.
Supposedly I will be speaking to an engineer, I truly hope he is the famous one ?. Old inverter is going back to California for him to inspect it and hopefully come up with a solution. Someone correct me but I was under the impression that Voltronic made Growatt, MPP, the EG4 units and SunGold...
81-104 watts is being drawn from the grid whether the unit has it's outputs on or off. The 9 watt background draw is the clock of the stove and the electronics on the heat pump hot water heater.
I tried using an Xstar V4 18650 charger off the inverter a few days back but the transformer was letting out a whine and the display was flickering. Switched it back to bypass, no issue. Just going to leave it there until we get an answer from Sunpower. Most other ac/dc chargers I tried worked...
Meh, they did just respond with, "You are the first to show an abnormal waveform. Keep waiting, the engineers need to verify the issue it's going to be a few more days". Which ok I get it but if the waveform I sent is not what they said the spec is just replace the unit or send me the inverter...
What's odd is that we have this exact same configuration (grid connected reliance transfer switch with pass though neutral) running in our cabin and have 0 issues. That is a small 3kw Growatt though that only runs at about 5% capacity max. It was already installed when we purchased it, I never...
So with the grid off the load shifts to the battery. Looks like all the standby power usage of the unit is drawn from the grid if it is available with no option to disable it. THAT IS DUMB!
@Will Prowse By any chance did you check the output waveform of the SP6548? I am already locked into this unit under my existing permits so before I go and pay for a replacement to avoid months of downtime I would like to know if this is an issue isolated to this unit. Figured it's a long shot...
Unfortunately I have it set to solar charging only. But, funny you brought that up. I did notice last night that even when set to solar only the BMS was reporting more amps than the panels were producing. I threw my amp clamp on the input and saw 2 amps coming in on the mains connection. Now is...
I have 45kw of battery... I am not worried about that. If it defaulted to grid for that load there should be an option to put that load on the solar/battery. If it is on SBU it should default to that automatically.
I sent them an email. They are still "working" on a resolution for the flickering lights so I have little faith this will go anywhere. The point of a hybrid unit is to use as little grid power as possible. Drawing the standby load from the grid when there is solar and battery available makes 0...
good to know! I think it's just a dud. Hopefully we can resolve this amicably. So far it's like pulling teeth. Again, the language barrier is tough especially when you get into technical topics. Will update when I find out more.
Just gave it a try with a 1200w space heater, no change in the flickering. Adding an incan bulb to places like an office with just 1 fixture kinda stinks. Point is to save energy not use more to help the inverter figure things out. If my other cheap pure sine inverters run these loads directly...
They sent the wrong range scope. But the drifting back and forth show the inverter clearly has a problem. I tried it with no load, 3kw resistive, 500w resistive, no pv or grid.. nothing changed. Every anomaly in the waveform coincided with the lights flickering in that room. The video I took on...
It is a clone. They have different components and use a daughter board that the original design does not need. After months of fighting with SunGold over flickering lights, seeing people here complain about similar issues with the EG46500EX I think we have all learned a lesson about clones. Not...
Unsure how those are wired. Just saying how I tested it to compare apples to apples. 99% certain the problem has been resolved. Tested everything that has been giving me problems and so far no issues. Need to bring a scope home from work.
They can not all be the same electronically. If they were we would not have these issues with some brands and not with others. My loaner MPP has no daughter board, different fans, different fan cutouts, 1.2 amps less draw at idle and best part... no flickering lights or error codes all on the...
I don't believe a passive filtering device would be able to correct the problem. When we were on gen power I had to install that unit to get a clear image and eliminate hum. It wasn't cheap but it solved the problem 100%. Fluctuating dirty power in, crystal clear120v 60hz on the output. Well...
These short clips were created to send to the manufacturer as they are they are now non-responsive. I ordered directly from their site and paid with PayPal, am debating on opening a case. I will give them another day. Building inspector wants the entire system removed if we can not do a 1 for 1...
Afraid I am going to be told it's a "characteristic" of the HF inverter since I see tons of posts about this on Growatts and no one seems to have figured out a fix.
Hard to see due to the phone camera shutter speed but it is there
It's easier to see when I did not have the correct range scope. Dances around like a wet noodle.
I am STILL going back and forth with them! Basically it's a design defect that they claim goes all the way back to the base design. IE no way to fix it. But, they are continuing to use this design..... wth
I saw Will's review of the new EG4. He noticed a circuit breaker on the input and some changes in the inverter caps and mosfets as well as a different firmware. This SunGold unit also has the breaker on the input and the firmware is different than the LV and the EG as it shows revision 69. It...
It is easily visible on the scope but my camera just doesnt capture it well. I did see the exact waveform anomalies on a YT video about Growatt flickering. He said his stabilizes after some time but mine does not.
That is exactly my issue. The majority of the first floor lighting is tied into the family room outlets. Kitchen cans are tied into the dining room lights and receptacles. It makes 0 sense but that's how the do it in the US. I really don't have that option unless I rewire the house and that...
Something is up.. nothing would run off that waveform. Also the first waves looked like modified sinewave.. weird. Is the power supply isolated? I used an isolated power supply and connected my scope to hot and neutral not just 1 leg.
The flat spot is clipping due to the lower range of that scope. That is why I found a scope with a larger range. You can see the shifting in the wave better on the scope with the blue backlight.
That is not normal, I just double checked and mine immediately kicked over to bypass when I flipped the battery disconnect. I noticed this when I installed the shunt, it kicked back to bypass when I killed discharging through the BMS. It did have a bit of a longer delay than I would like though...
I would be OK with an inline isolation transformer but I can't find anything meant to be hardwired under 1k. Just doesn't make sense to put a 1k bandaid on a 1.3k inverter.