Fuse and Isolator alternative?

Beavo

Didn't, don't, won't know what I'm doing.
Joined
Jan 28, 2024
Messages
70
Location
Bristol
Between the batteries and inverter, is there any reason I can't replace these...
1000010933.png
(Mine is 200 amp)

1000010932.png

With this...

1000010934.png

Saw a guy on YouTube with this setup and it seems much cleaner.

Cheers
 
None at all - if you can find a "UL" listing on that breaker, and if 200A OCP is suitable substitute for 30A OCP, and if voltage and AIC rating are high enough.

Those no-name breakers are highly suspect. Good brand names are available.
They are thermal only, slow trip. The fuse will fast blow at some current above 5x its rating. Quality breakers are also available with magnetic fast trip. My new love is magnetic-hydraulic breakers, rather than the thermal-magnetic I've used before.

By the way, if you want a precharge circuit, some rotary switches are available with off-on-on configuration, convenient to implement it with a resistor.
 
A couple points.

1) Be sure to only buy name brand on that style breaker. (Blue Sea is a good brand) The knock-offs are notorious for being dangerous.
2) The ANL fuse has a very low AIC rating. It is generally accepted that the main battery fuse needs a class T fuse with the 20KA AIC. (There is some debate about whether 20KA is needed but not much debate that at least 10KA is needed for a single battery and 20KA is need for parallel batteries.
3) I don't know what the AIC of the breaker is, but that should be checked.
 
A couple points.

1) Be sure to only buy name brand on that style breaker. (Blue Sea is a good brand)

Blue Sea only seem to go up to 150 amps with surface mounts and their website is painful to navigate on a phone.

Are there any other reliable manufacturers that make a 200 amp version?

Cheers
 
None at all - if you can find a "UL" listing on that breaker, and if 200A OCP is suitable substitute for 30A OCP, and if voltage and AIC rating are high enough.

Sorry, I'm new to the forum and haven't picked up the lingo yet.

I understood the "None at all" bit.

I didn't understand anything after that.

Thanks anyway.
 
Sorry, I'm new to the forum and haven't picked up the lingo yet.

I understood the "None at all" bit.

I didn't understand anything after that.

Thanks anyway.
UL is Underwriters Laboratories.
They do testing on products to make sure that they meet minimum safety protocols in order to be used in the USA, at least correctly.

That isn't to say that there aren't products out there that aren't UL certified that probably won't be "good enough" but for serious installs (especially something that needs to be inspected by an electrician) you likely can't legally use anything at all that isn't UL listed.

OCP = Over Current Protection

AIC = Amperage Interrupt Current



That device you posted is called a MRCB (Marine Rated Circuit Breaker) and it's a close of a Bussmann unit.
 
The fuse and the disconnect switch have a number of ratings. So do breakers.

Fuse: Amps, voltage, AIC (ability to open with high current short circuit) which varies with voltage, current/time curve.

Switch: Current, voltage, whether it can interrupt current or only be opened with zero current.

Breaker, both of above.

What is your system voltage? What battery do you have?
Lithium batteries can deliver massive current, may cause a fuse/switch/breaker to draw an arc and burn. When connected to an inverter, which has capacitors, a brief surge of several thousand amps and damage things.

You need full specs for all the involved parts to determine if the work together.
 
Blue Sea only seem to go up to 150 amps with surface mounts and their website is painful to navigate on a phone.

Are there any other reliable manufacturers that make a 200 amp version?

Cheers

Get on a computer. Easier to use a mouse, save links and screenshot or print to files. Draw schematics, etc.

Blue Sea has good stuff, as does Midnight Solar. Some breakers are in a different format, DIN rail or bolt mount, and have higher rating and additional capabilities beyond those flat thermal breakers.

For a small 12V system, brand name breakers of that format may be sufficient.

Photos, part numbers, links to data sheet are useful for people to help. That includes your existing equipment, not just the protection devices.
 
Here's a 200a rated version-

"
Maximum Voltage48V DC
"
"
Interrupt Capacity
information.png
5000A @ 14VDC
3000A @ 28VDC
1500A @ 48VDC
"

(Note that doesn't mean a 48V nominal battery, rather one that never exceeds 48V, e.g. 36V nominal.)

Compare interrupt capacity to short-circuit current your battery can deliver.
A 100 Ah 12V AGM battery can deliver 4000A. Lithium, I think much more.
So we prefer higher performance fuses and breakers.
 
Just a small setup.
Going to be expanding it a bit more.
Everything I have is in the photo other than the 4 160watt panels in parallel.
1000010940.jpg

Cheers
 
12V system, you can get away with a lot more. But I do think LiFePO4 batteries could deliver high short circuit current if BMS failed.

So I'd prefer an expensive breaker, or a fuse. Be sure to use appropriate fuse holder. In particular for MRBF which looks like it could bolt directly to battery, but I think that would bypass/short the fuse.



 
12V system, you can get away with a lot more. But I do think LiFePO4 batteries could deliver high short circuit current if BMS failed.

So I'd prefer an expensive breaker, or a fuse. Be sure to use appropriate fuse holder. In particular for MRBF which looks like it could bolt directly to battery, but I think that would bypass/short the fuse.



Thank you very much for taking the time to do that.
Cheers
 