That will work but it isn't a good idea, at least with lead batteries as it will cause imbalance, especially if you have significant loads. Lithium I do not know as I am new to that. Better would be a 48/24V to 12V converter to cover the 12V loads.
yesbeat you to the drawing . Yes I know its a bit primitive but I'm at work right now so I just scribbled it really quick. So if I had 4 charge controllers the number of batteries doesnt affect their ability to charge evenly. If I wire everything in parallel to keep it 12v, the 4 solar chargers will charge any quantity of batteries evenly?
absolutelyAlso guys. I was wondering if I should wire everything to a central distribution block rather than running the charge controllers to the batteries than the batteries to the inverter?
As the OP stated in his first post, he is aiming to run 4x SCC @12v each, so he could in effect run one controller to each battery from each bank of panels, combine 4x 12v batteries in series to a 48v bank, draw the small internal 12v loads from a single battery and span the 4x batteries for the 48v inverter. Providing the internal 12v loads aren't high the batteries wont go out of Ballance plus he will have an SCC per battery to keep each one charged.
As the OP stated in his first post, he is aiming to run 4x SCC @12v each, so he could in effect run one controller to each battery from each bank of panels, combine 4x 12v batteries in series to a 48v bank, draw the small internal 12v loads from a single battery and span the 4x batteries for the 48v inverter. Providing the internal 12v loads aren't high the batteries wont go out of Ballance plus he will have an SCC per battery to keep each one charged.
Again -the inverter you infer will need much larger cabling than 0 or 1 awg to avoid massive voltage drop.Also the run from the battery bank to the inverter would be very short. Probably about 4 feet or so. I'd plan on using 0 or 1 AWG wire, as I know that 3000watts (just for the AC kicking on) is quite a bit.
There is no cutting corners on equipment installation -if the desired outcome is to use the 4k / 12v inverter and running AC. It will require more battery, very large cabling, and appropriate over current protection(OCP)(Fusing). That is -if you want a safe and reliable system.I'm not planning on running the AC off batteries much, if at all. But I figured if I'm spending a decent amount of money, I'd like to at least have the option every once in a while. As I mentioned just above I won't ever come near 4000watt draw. The 4kw inverter would just be to make sure the act of the AC powering up won't damage the inverter. I know most inverters have capability to double the output for usually 3 seconds or so, but I figured a powerful enough inverter would be a "better safe then sorry" type solution.
Again -the inverter you infer will need much larger cabling than 0 or 1 awg to avoid massive voltage drop.
There is no cutting corners on equipment installation -if the desired outcome is to use the 4k / 12v inverter and running AC. It will require more battery, very large cabling, and appropriate over current protection(OCP)(Fusing). That is -if you want a safe and reliable system.
Seems we are going around in a circle......Yes, I'm aware. That is exactly what my question is lol
Unfortunately it does. Thats why I removed the AC from the equation. I got one question answered regarding the equal charging of multiple batteries. Now I'm just wondering where people would put fuses, and possibly isolators in the "circuit" that I drew above, and whether or not I should wire everything to a center Distribution Block or just keep wire runs separate.Seems we are going around in a circle......
Before you get too deep into design you really need to do your energy audit. There is no way to design a system without a firm handle on what you need. This will mkae sure that you get a system that meets your needs and doesn't spend more than you need to.
My system is designed off the number of panels I can fit on the roof. I want to have the maximum capabilities for what I can fit on the camper. The battery bank size would be partially "designed" to accept the charging current from the solar, and I'd like to be around 300-400ah just because. The Renogy 3000w inverter would also be overkill just so I don't ever overload it. Its all probably WAY overkill but again, I'd rather be safe than sorry.
But if you use math, you can KNOW the answer. If money is no object and you are OK with spending it without knowing if it will work for ya, carry on. An energy audit is simple and you may find for example that you need less than you thought. Or that you won't have enough. It may allow you to make decisions on equipment that you won't have to replace or upgrade. You may be able to put part of the system up and leave it easy to expand if needed. It could save you a lot of time, effort and money.
I'm well aware of the requirements regarding powering a 3000 watt inverter, and I will take all the proper precautions to do this safely. My question is not about wire size but more about circuit configuration and placement of fuses and use of battery isolators (if needed).No math typically equals a system that doesn't perform to expectations. 3k inverter needs serious size and quality cabling to fully perform. Installing to "partially" perform without a derating program is a fire hazard -plain and simple.
I agree with @boondox regarding the need for an energy audit and a wish list of items to power to avoid excessive duplication and lack of performance.
Example 3k inverter wired with to small of cable is a fire hazard.