Fully updated both batteries. I was on old 3.32.
Also looked at the issue of resistance so I swapped the cables around. (Was POS on top left and Neg on bottom right)
Ran it for 10 days like this. And 15 or so days of down to 15/20% and back to 100 daily. Settings 56.4 float 56.4 bulk.
At around day 8/9 it reached 99.3% on the battery with the laggy cell doesn't go higher than that. And 56.8 is most I can go on the bulk without alarm(3.55v is alarm parameter).
View attachment 208961
Photo was at the very end of the bulk charge.
View attachment 208964
Also note as it goes down to float voltage. The battery with the lagging cell also consistently says its losing current. The normal one doesn't do this. It's an insignificant amount of capacity though.
View attachment 208965
And at float voltage. Seems I still get my full capacity at this time. Just hope it doesn't get worse over time. But so far so good as it is. Wil keep it on USER settings as the voltages in eg4 are still too high for the alarm/protection settings in place.