Any better alternative to MPP PIP 2724? 24v, 2,700w All-in-One unit

I have another "dumb" question: When watching CleverSolarPower's videos, he states max for 24v system is 2,000w inverter. Are there any issues running 24v with 3,000 inverter such as the Midnite?
No this is just an opinion. Its really just for sizing components and wiring. I run a 4000W 24v setup and wouldn't change a thing (I run Lead acids though). Even 6k @ 24V is not uncommon.

With only 2 of those batteries in series, you might bump into the max discharge rate if its only 100A BMS. So 100A @ 24V = 2400W. With no PV input at night you are limited to 2400w continuous. (They can surge to 280A for 5 seconds).

LiTime says you can do up to 4 in series. Yes over time you may experience balance issues, or you may not. Lots of folks do it. I think it mostly depends on the charge cycles and the ability to charge to full each day.
 
Incidentally I run the 3kW SRNE (PowMr) high PV voltage model. This afternoon I have on my 8000btu Aircon. You will see that under load the PV, with my battery full, does all the work of running it. The meter at 247w PV incoming is with the AC compressor cycled off just fan operating. When compressor cycles on you will note the incoming PV jumps up and the amount is slightly more than the load meter due to operating losses.
 

Attachments

  • IMG_20240415_143943113.jpg
    IMG_20240415_143943113.jpg
    118.4 KB · Views: 4
  • IMG_20240415_144010382.jpg
    IMG_20240415_144010382.jpg
    116.1 KB · Views: 5
  • IMG_20240415_144004465_HDR.jpg
    IMG_20240415_144004465_HDR.jpg
    156.5 KB · Views: 5
  • IMG_20240415_144017854_HDR.jpg
    IMG_20240415_144017854_HDR.jpg
    233.2 KB · Views: 5
No this is just an opinion. Its really just for sizing components and wiring. I run a 4000W 24v setup and wouldn't change a thing (I run Lead acids though). Even 6k @ 24V is not uncommon.

With only 2 of those batteries in series, you might bump into the max discharge rate if its only 100A BMS. So 100A @ 24V = 2400W. With no PV input at night you are limited to 2400w continuous. (They can surge to 280A for 5 seconds).

LiTime says you can do up to 4 in series. Yes over time you may experience balance issues, or you may not. Lots of folks do it. I think it mostly depends on the charge cycles and the ability to charge to full each day.
Okay cool. Thanks for this information. That helps a lot to know the larger inverter is not an issue. Since it's my first solar build ever I think the 3000 inverter with the 2400w 100a batteries will be perfect for my needs. I get like 6 or 7 hours of direct sun in my backyard so should be able to use solar to power my loads continuously during the day. And then switch to battery and/or grid at night. Does that sound correct? Apologies if these questions are elementary but before last week I didn't know my watts from my amps! ...LOL
 
I looked at that for my cabin years ago and opted to go with the Growatt 3kw 24v instead. I didn't need tge outlets and at the time the Growatt was about $100 cheaper, let me put in 2kw+ of panels, and had that extra few hundred watts of overhead. No regrets so far.
 
Incidentally I run the 3kW SRNE (PowMr) high PV voltage model. This afternoon I have on my 8000btu Aircon. You will see that under load the PV, with my battery full, does all the work of running it. The meter at 247w PV incoming is with the AC compressor cycled off just fan operating. When compressor cycles on you will note the incoming PV jumps up and the amount is slightly more than the load meter due to operating losses.
This is exactly what I want to do! The AC unit draws about 900w and I just want to use solar during the day to power it
 
Rednecktek, you said you went with the Growatt. Between the MPP LV2424, Midnite MN3024DIY, and Growatt SPH 3000TL would you still recommend the Growatt?
Yup. Midnight was outside my price range and "coming soon" and the Growatt has another 600w of overhead to work with. It also has a lower starting voltage on its MPPT than most other AIOs which helps with the constant overcast I have to deal with in the PNW. The Growatt also supports more solar (2000w) and a wider MPPT range to work with.

Having said that, the Midnight looks real nice but it's a brand new product so I'd want to see some real world reports. Seems like a low end version of the PowMr version with lower starting voltages.

I've had the kinds of overcast where a pair of 200w 39VoC panels in SERIES were only putting out 15v.
 