Must I use "PV" wire for runs inside attic space?

inowhavesolar

New Member
Joined
Jun 15, 2022
Messages
11
I need to run wire from panels on roof, about 60ft, through attic space, to unfinished garage to inverter. There's an "attic tunnel" which connects main house to detached garage. Do I have to use #10 "PV wire" through the attic or can I transition in the roof box to standard #10 THHN wire?
 
I need to run wire from panels on roof, about 60ft, through attic space, to unfinished garage to inverter. There's an "attic tunnel" which connects main house to detached garage. Do I have to use #10 "PV wire" through the attic or can I transition in the roof box to standard #10 THHN wire?
I believe NEC code requires DC inside a dwelling to be contained in metal conduit or equivalent.
 
Last edited:
I can assure you from personal experience - if a wire can be accessed by a rodent - they will find it and chew through it.

No matter what anyone wants to believe, rodents can and do get literally anywhere and have a passion for chewing through wires.

They also love to chew on roofing materials including tar paper.
 