60 ft

e67

New Member
Joined
Jul 7, 2022
Messages
133
is 10 ga solid copper romex ok for a 60 ft run..?300 volts dc. 11 amps
 
10 AWG wire nominally has 1 milliohm per foot resistance.
60 feet would have 60 milliohms of resistance, but you have to double that for both wires.

So 0.120 ohms total for the 60 ft run (2 wires)
Voltage drop would be (0.120 ohms)(11 A) = 1.32V
Power lost is (0.120 ohms)(11 A)(11 A) = 14.52 Watts lost to heat in the wires
Sounds ok to me

alternatively, use this: https://www.southwire.com/calculator-vdrop
 
Last edited:
Yes, more than ok on wire size. But there are few applications where Romex would be appropriate for PV in the USA. We are technically supposed to put PV DC in metal conduit indoors.
 
of course it would be in conduit..300v DC.
6-7 390 watt in series ..
 
I was gonna do it until I knicked a bit of my underground UF-B with a shovel and that's how I learned to just use conduit in the future.
Did that with my septic pump UF-B wiring, the builder put them 6” down!
remember Kids when in doubt call 811. I do that everytime somebody pisses me off... I don't want to cut any com cables or underground power lines!
 
remember Kids when in doubt call 811.
Sadly, they will only come out and mark utility lines (electrical, water, cable, phone, gas, etc.).
Privately buried lines like well and septic are not traceable.

However, I have purchased tracer tape for my PV to house buried run, so someday in the future it can be found.
Link:
 
Last edited:
Sadly, they will only come out and mark utility lines (electrical, water, cable, phone, gas, etc.).
Privately buried lines like well and septic are not traceable.

However, I have purchased tracer tape for my PV to house buried run, so someday in the future it can be found.
Link:
I think thou hath misunderstood my jollification attempts. :whistle:
 
gotta get them to drop lines prior to digging holes. A 6 x 2 x 6 hole can take out a lot of wiring.. plus I don't want the critters digging somebody up 2 or 3 months later.
I found it easier to use the 36 inch post hole auger bit with an extension.

Makes em stand up for eternity.
 