The running wattage is not a problem but the starting wattage may very well be. The more load that motor has to lift the more that initial surge will be. Your main concern will be to determine that that Surge Wattage which will more than likely be nearer 1500-1700W but could be as high as 5X the running watts.
The Inverter chosen will have to support that surge rating. You "may" be able to use a Modified Sine Wave Inverter as it is just a motor and intermittently used for short periods only (the few minute to open/close).
12V systems can support up to 2000W comfortably without issues.
2000W @ 12V = 166.6A uncorrected. being pulled from the battery.
This should be fused at 175A.
Battery should be able to support a 175A Discharge rate. Can be Lead, AGM or other.
Battery Size at 12V would not have to be huge either... But 50AH would likely do it fine. (just for the door opener, not extras).
** Will just reviewed some Miadi ? or similar low cost but Really Good assembled batteries from Amazon. Check his videos.
Solar Panel - SCC
There are now AIO's "All in Ones" for 12V <2000W which are very affordable & simple to install and saving a lot of extra hassles & bits too.
A very respectable example here:
https://usamppsolar.com/product/pcm60x/
Solar Panels (do NOT buy 12V panels !) can be had easily enough, used or new... Many buy used from companies like
SantanSolar with great results. NOTE: DO NOT BUY Unlabelled / Unbranded panels NOR "House Branded" panels unless a warranty is explicitly specified.
Racking/Mounting will be required (if mounting on a roof, panels must be 12" below peak and 12" above the bottom edge and provide a MIN of 6" clearance between panel & roof surface) This is to prevent the panels becoming Sails in a windstorm, to stop them from "catching" stuff and the clearance to allow for heat dissipation and airflow (it gets really hot under panels).
Hope it helps, Good Luck.