Noted, should I add in 15 amp fuse breakers on the positive wires coming from each string of panels before going into the mc4 connectors?Don’t see fuses on the three string of panels. Two does nto reroute fuses or breakers. Three or more does.
200 ah of batteries does not seem a lot for a 3000 watt inverter. That is based off your power consumption.
I‘m not sure a SCC set to 24 volts will output 12 volts on the load Terminals. That will be in the owners manual.
For Battery monitor, that’s your choice. The SCC display only shows amperage to the system. This can be taken up by loads. For a monitor, it will give you an accurate state of charge and whether your loads are pulling more than the SCC provides and using battery power negative, or more than the loads and the battery is charging positive amps.
Technically yes but I would skip it for this low power set up.Noted, should I add in 15 amp fuse breakers on the positive wires coming from each string of panels before going into the mc4 connectors?
Whatever the instructions say. The shunts I’ve used get installed on the negative side.Would I use a battery monitor shunt to hook the monitor up on the negative wire between the charge controller and battery bank?
Read up on this. Short answer is with lithium yes, and with lead acid, there’s a bit of debate. I think its not wise to add lead later.Does it seem like I would be able to add 4 more batteries in the future to increase our stored energy from 4.8Kwh to 9.6kwh?
So, you don’t think three sets of panels in parallel need breakers? Like to hear why.Technically yes but I would skip it for this low power set up.
Barely over the typical 15 amp short circuit rating and only 112 volts. With a little resistance the fuse may never open.So, you don’t think three sets of panels in parallel need breakers? Like to hear why.
You want 1AWG, not 4AWG, between the batteries and between the battery and inverter to safely handle the amperage.
I find it unlikely the load terminals of the SCC will be 12V while hooked up to a 24V battery.
Your 12V fuse box wiring doesn't make a lot of sense. The fuse box needs both a positive and a negative wire. What kind of outlet is that connected to the SCC load? What's the point of that bus bar on the negative SCC load?
I think it would be a much better plan to have proper battery bus bars that can be used to connect the inverter, the SCC, and most likely a 24V-12V DC-DC converter for your 12V fuse box. Then you can have a proper battery fuse between the battery and positive bus bar. You can have a shunt between the battery and negative bus bar.
Which SCC are you going to use? What is its max battery current output?
You want 1AWG, not 4AWG, between the batteries and between the battery and inverter to safely handle the amperage.
I find it unlikely the load terminals of the SCC will be 12V while hooked up to a 24V battery.
Your 12V fuse box wiring doesn't make a lot of sense. The fuse box needs both a positive and a negative wire. What kind of outlet is that connected to the SCC load? What's the point of that bus bar on the negative SCC load?
I think it would be a much better plan to have proper battery bus bars that can be used to connect the inverter, the SCC, and most likely a 24V-12V DC-DC converter for your 12V fuse box. Then you can have a proper battery fuse between the battery and positive bus bar. You can have a shunt between the battery and negative bus bar.
Which SCC are you going to use? What is its max battery current output?
3000W / 24V = 125A. Take into account some inefficiencies and call it 150A. Looking at a good wire/amperage chart such as that provided by Blue Sea Systems gives you a recommended wire size of 1AWG. Then you want to pick a proper fuse for the inverter to protect the wire. Use a max of 250A fuse on a single 1AWG wire or about 175A if it's bundled with others. Pick a fuse bigger than the loads to avoid nuisance trips. So I would pick a 175A fuse between the inverter and battery.When I use a wire size calculator should I be considering the amperage to be 1.56 times the amperage I'm expecting for safety reasons, and that's why I should use 1AWG?
What is the output current to the batteries for this SCC? That will determine whether your proposed 8AWG is sufficient.I was going to use the Midnite Solar Classic 150MPPT
Your updated diagram leaves me with a few comments:Does this look more reasonable?
60A would be better assuming the wire is safe with that. 50 is too close to 45 and you run the risk of nuisance trips.2. A 50A breaker between the SCC and batteries as the SCC will be giving a max of current of 45A to the batteries that ask for 40A.
A single SOK battery supports 100A max continuous discharge and wants a 40A charge. With two in parallel you can double both of those. So your 2S2P battery setup is fine with 200A continuous discharge and 80A charge, all at 24V.I have 4 SOK batteries but they are the 12V 100Ah, rather than the 12V 206Ah. I think this means my batteries max charge current will be 100A, and their preferred charge current 40A when wired in 2S2P.
Just to triple check, this was the chart I was referencing which is under the specifications for the SOK batteries found through one of Will's links. Am I looking at the wrong chart? I just really want to be sure of what they should be charging at60A would be better assuming the wire is safe with that. 50 is too close to 45 and you run the risk of nuisance trips.
A single SOK battery supports 100A max continuous discharge and wants a 40A charge. With two in parallel you can double both of those. So your 2S2P battery setup is fine with 200A continuous discharge and 80A charge, all at 24V.
Do you think it would make more sense to use a Victron 70amp charge controller then? Would I be able to program (as a beginner) this controller to suit the SOK batteries?A couple of comments:
1) The SCC may not produce as many amps as the panels are capable of. If you plan this, than fine. Math in my head says for every 200 watts of panels you can charge a 24 VDC system at 6 amps. Math in my head puts this around 65 amps.
Do you think it would make more sense to use a Victron 70amp charge controller then? Would I be able to program (as a beginner) this controller to suit the SOK batteries?
Yes for my Victron SCC you could.Would I be able to program (as a beginner) this controller to suit the SOK batteries?