The Victron Multiplus 12/3000 has an efficiency of 93%. Most LiFePO4 batteries spend their life around 13 volts, not 12 volts (but 12 volts is common to use in these calculations). That puts the maximum (continuous) amp draw at closer to 496 amps (6000 / .93 / 13). That's still quite high, but each inverter would be half that, so call it 250 amps. The manual calls for a 400 amp fuse to on the cable to the inverter.
The calculator linked below says that 250 amps @ 13 volts for 10' round trip could use 2/0 cable for only 1.53% voltage drop.
The Multiplus can accept two cables on each polarity. If the existing cable isn't enough, add a second one.
baymarinesupply.com
Interactive Wire Size Calculator
Battery Chargers, Inverters, Solar Components, and Wiring Supplies for Boats, RVs, and Off-Grid Applications.