permitted solar with Net Metering Credit.I'm not sure of your system topology.
Put in the grids as much as I can.
No limitation needed/wanted.I think you have a grid panel to run part of your home that the MR would supplement by monitoring CTs to prevent sending extra to utility.
I have 17x enphase (ML & IQ) micro inverters, a 3.8kW fronius string inverter, 2 sunny boy (7.7TL & 2kW HF) string inverters _and_ my MR
I can only find 1 CT at the moment, it clearly came with 2 ;-)
My MR is mounted about 45 '/15 meter cable length away from my main breaker panel.
Correct.Then you have a CLP that the MR feeds from LOAD1.
It is, but the AFCI breaker trips because it detects "an arc" of some kind, maybe because the MR has to invert and has to find the neutral level to between L1 & L2 ?With main grid panel breaker flipped off, the MR is NOT enabling EPS from battery/PV alone?
I have Neutral of the CLP connected to the neutral of the MR *AND* #4 wire (95 amps rated) to the main breaker panel neutral.
Just to make sure the neutral is not "floating"
I think I will replace the breakers with "old school" non-arch breakers.
can you define "run the EPS off batt/pv"?Currently, I have NO grid connection. My breaker panel is hooked to LOAD1. I'm using DIY lithium but with LEAD-ACID selected. I'm using SELF-CONSUM mode.
With main grid breaker off, MR powered off, If you unplug the two CTs, then connect batt, then PV, will the MR run the EPS off batt/PV?