I just want to confirm something with the EG4 3kW Off-Grid Inverter... in the manual it says "PV Array MPPT Voltage Range" is 120VDC~450VDC.
This means that you must supply at least 120V from the panels before charging will start, correct?
So if I had, say, three panels with VOC 50V, I'd have to put three in series (for a VOC of 150V) before the MPPT controller would start charging the battery. Do I have that right?