DC Breaker combiner box confusion

tonyg

New Member
Joined
Apr 5, 2022
Messages
136
Hello there,

I need a bit of help to understand the schematics of the following from an official manual:
1666009175677.png

What does Midpoint earth mean? It is first time I see this term...
I've got the iC60H, which was confirmed by Schneider to be the same with regards to specs and requirements with iC60N. I'm using it in my combiner box as follows:
1666009455537.png

Wondering if I'd need to change anything based on the manual with regards to midpoint earthed...

Thank you kindly,
Tony
 
As you can see in the schematics posted initially regarding the combiner box.
Then no, you have it correct.
And as far as "midpoint earthed" is referred to in this diagram. It's just the ground.
 
Thank you sir, glad to hear this .

And to double-check that I understood everything right (I'm a DIY-er learning every day), in the breaker, the positive has to come in in the up right hand side and negative up left hand side? Load (i.e.: MPPT) comes at the bottom of it.

IMG_20221017_154002.png
 
Thank you sir, glad to hear this .

And to double-check that I understood everything right (I'm a DIY-er learning every day), in the breaker, the positive has to come in in the up right hand side and negative up left hand side? Load (i.e.: MPPT) comes at the bottom of it.

View attachment 116729
Correct
 