Saw this video on Victron's 'dynamic assist' feature that provides a 'rate of change' limiting on AC input. This feature is probably most useful for inverter-generators in ECO mode where generator rpm is modulated based on AC output load on generator.
The difference between 'limiting AC input current' and 'dynamic assist' is limiting AC input does not start the inverter reaction time until AC input current limit is reached, while the 'dynamic assists' starts the inverter supplement as soon as AC input current starts to rise before AC input current limit is reached, then gradually backs down inverter supplementing assist to let AC input take the limit of AC input. This gives the inverter feedback control a jump on covering a sudden surge, not having to wait until AC input limit is reached before it gets involved. This should reduce initial surge leak-through to generator, like starting an air conditioner.
The obvious advantage to inverter-generator variable rpm ECO mode is lower generator noise and some fuel savings.
Disadvantage is, in response to a step increase in AC load, the inverter-generator has to increase its engine rpm which takes a second or two. During this rpm ramp up, the generator's alternator is unable to supply the peak load current so the output AC sinewave voltage peaks from inverter-generator's inverter are clipped.
For a conventional synchronous fixed 3600 rpm generator there is a lot more stored mechanical energy reserve in the 3600-rpm rotating engine flywheel. Just need a good stable engine speed governor control that does not vary with generator loading to keep generator AC output frequency from varying too much, which if more than about 0.3% per second wobble, will cause inverter to be unable to track phase with generator and causes inverter to release from generator.