Which 3 pole transfer switch did you go with? I'm interested in getting a 3 pole 100A too.I went with a three pole double throw so that I'm switching neutral as well as both legs, but I only needed 100a. A 200a is around $1,900. But yeah, they take up some space, even the two pole.
I do not know why it would be an issue. 120 volt switches do not switch the neutral. The circuit breakers do not cut off the neutral. My inverter does not cut off the neutral when it goes off grid. The only caveat is that I have no idea if there is a code requirement one way or the other.Is sharing a neutral between the power grid and inverter not an issue? In the event of a power outage isn't that an issue?
There's a lot of discussion on the pros and cons of a three pole vs a two pole. Without getting into all that, I opted for the three pole 100a Siemens. The best deal I found was Home Depot.Which 3 pole transfer switch did you go with? I'm interested in getting a 3 pole 100A too.
Based on the specs I don't see any reason it wouldn't work. That said, if you look at the pictures with the cover open the Siemens looks like a lot more switch to me. I didn't see the GE when I was looking or I certainly would have considered it. Maybe someone on here has experience with both.I have been looking at this one:
https://www.homedepot.com/p/GE-200-...ency-Power-Transfer-Switch-TC10324R/100150463
Yeah one is two pole the other three. I need 200 amp.Based on the specs I don't see any reason it wouldn't work. That said, if you look at the pictures with the cover open the Siemens looks like a lot more switch to me. I didn't see the GE when I was looking or I certainly would have considered it. Maybe someone on here has experience with both.
I'm gonna say that's a yes, depending on the price.Is there a market for used 200a manual and automatic transfer switches. We have about 10 each.
I just installed a 15k and used an Eaton safety switch/shutoff, 600v 200A, fused, 2 pole, as main shutoff and first means of disconnect. For switching between grid and and the solar to feed my load panel I opted for the 2 pole double throw/3 position, 600v, 200a non fused, transfer switch from GE referenced in this thread.For the Solark 15k, do you only need to switch the 240v black/red? Do you also need to switch the neutral? Maybe not?
I know this is an older thread, but no, it is not an issue to share. In most cases you are better off sharing than switching the neutral. If you do switch the neutral you need to have an overlapping neutral-- no "off" position, and you need neutral-ground bonds on both sources. Current will always flow back to the source, so if it is the grid then that will be the source, and if it is the inverter that will.I see everyone advising to use a 2 pole double throw transfer switch. Is sharing a neutral between the power grid and inverter not an issue? In the event of a power outage isn't that an issue?
Yes, You just need a 200A circuit breaker,why not make one by your self. It will cheap a lot.This is very interesting, hadn't considered it. Time to do some reading!