I have a 48 v off grid system. I’m having issues not getting power to receptacles in wall. I have an earth ground rod on the panel box. Should I be grounding it at the inverter instead?
Does the AC IN have a lug for Ground? Inverter ground is normally a separate lug attached directly to the enclosure, but not always.From the AC in to the ground bar in the panel box?
Does the AC IN have a lug for Ground? Inverter ground is normally a separate lug attached directly to the enclosure, but not always.
Could you post a wiring diagram from the inverter manual or at least provide a model number for the inverter.
This implies that you have no grounding system. (N/G bond)I tested each leg at the box each has 60 combined 120
I truly hope not.I’m getting power through the breakers even with all the breakers off including the main
You might want to take a step back and call in an electrician or at least someone who knows their way around electricity. I’m all for DIY but that stuff can kill you and something’s not right here.I’m getting power through the breakers even with all the breakers off including the main
Yes, it is turned off now, but I did have it on when I was testing itFrom your picture in the other thread. What appears to be The main breaker is turned off.